If the max Ze for Tncs is 0.35 but you had a 1361 60amp fused isolator before the c.u with the 1361 having a max Zs of 0.56 (from the 80% chart) if the recorded reading at the c.u was let’s say 0.47 ohms would that now be considered to comply? i can’t see why it wouldn’t.
 
So is the fused isolator feeding some long tails/sub-main to the CU?

If the Zs at the end of the sub-main (i.e. at the CU) is measuring below 0.53 ohms (from my OSG Table B5) then everything is fine, assuming the earth/CPC is at least 10mm to meet adiabatic limit.

If it is some old installation with a 6mm CPC then the Zs limit is 0.47 ohms to meet adiabatic (see Table B5) but really in that case you ought to be looking to replace it with 16mm to meet other regs.
 
So is the fused isolator feeding some long tails/sub-main to the CU?

If the Zs at the end of the sub-main (i.e. at the CU) is measuring below 0.53 ohms (from my OSG Table B5) then everything is fine, assuming the earth/CPC is at least 10mm to meet adiabatic limit.

If it is some old installation with a 6mm CPC then the Zs limit is 0.47 ohms to meet adiabatic (see Table B5) but really in that case you ought to be looking to replace it with 16mm to meet other regs.
Yea that’s right and it is 16mm.
I’ll check that table myself, thanks for verifying though!
 

Reply to Exceeding the max Ze in this situation still be considered to comply? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Hi, first question on here in a very long time, I am hoping for some nice replies ?. It's been playing on my mind all week and can't seem to find...
Replies
12
Views
3K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
S
Hi. I'm newly qualified as a domestic installer so well aware I've got a lot to learn about the real world but... I looked over a friends...
Replies
51
Views
11K
Have a job where Ze is 0.36 ohms on a TNC-S with 80A BS1361 suppliers fuse. The general rule, as per OSG (page 11), is if Ze is below 0.35 ohms...
Replies
9
Views
12K
Deleted member 26818
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock