If you run the theoretical calculations for uniform soil you get less gain from length than the ideal R/l sort of expectation, but nothing that significant:
Here 'Row 12' was a rod calculation for 16mm diameter and soil resistivity of 120.492 (fudge to get 1m = 100ohm), and 'Row 13' just 100/length.
Formulae from here:
electrical-engineering-portal.com
Here 'Row 12' was a rod calculation for 16mm diameter and soil resistivity of 120.492 (fudge to get 1m = 100ohm), and 'Row 13' just 100/length.
Formulae from here:
Measurements and Calculations Of Earth Electrode Systems (BS 7430) | EEP
System earthing involves the provision of a connection to the general mass of earth. This connection should have a resistance not greater than that required to operate safety mechanisms to isolate the electricity supply from a fault situation.