I was thinking this PC.How were you measuring it?
Just wondering if using MFT's Zs/Ze and you are now seeing the impedance of the other rod at a TT supply end limiting the performance.
A number of years ago I had awful Ze readings on a TT. Extra rods made no difference. Next door happened to be having electrical work (from a far more experienced electrician than me) and he was having the same issues. He contacted the DNO and said they did something with regards their earth rod.
The results drastically improved.
Is there an earth rod at a transformer?
Would a test of the Ra by using a spike test kit be more reliable? If this result is much better than your Ze then it may indicate the above scenario.
I'm on pretty uncomfortable grown here though, so could be way off track.