Today I found a 466 ohm Ze. That's actually a new upper record for me. I assume the rod was completely corroded through.
So started to bang in some new 5/8ths rods.
1 rod - 180 ohms.
2 rods - 95 ohms.
3 rods - 93 ohms. Hmm.
4 rods - 92 ohms! Grrrrr.

I gave up then as I'd run out of rods. I also wished I'd saved the last two rods to install in parallel!
Has anyone ever had similar, and have I accidentally discovered the house is built on a potential sink hole?! Or maybe an old well?!
 

123

-
Esteemed
Arms
Reaction score
2,941
@timhoward 4 rods is impressive, unless they are only a foot long. Are you driving them into sand perhaps? Had a job recently where I got 4 rods in with relative ease, the 5th got about half way down. The area is built largely on sand I'm led to believe, and the reading wasn't anything great albeit about half of what you have.
 

pc1966

Esteemed
Arms
Reaction score
9,863
That is curious. Usually when you go deeper the conductivity increases as you have damper soil closer to the water table.

Your ability to get 4 rods, presumably 4' / 1.2m each, driven in is impressive! I wonder if they kept going straight down?

Putting in a mat, or even a trench around 0.5m deep and a run of several metres of bare 25mm or more copper wire, are other options to consider.
 
OP
timhoward

timhoward

-
Esteemed
Arms
Reaction score
6,519
Thanks for the replies. Yes, they were 4 foot rods.
The 1st one wasn't that hard. The other were much harder, about 5mm movement for each clout. It felt a lot harder than sand.

I had no need for it to be better than 100 ohms, I just get personal satisfaction from low readings. After the 2nd one I thought "I'll do one more and maybe get it to around 50 ohms and then call it a day."
Then when it didn't I got curious and thought I might as well try the last one.

Amazing how little impact sinking below 8' had. I'd be tempted to experiment, even at my own expense, and drive another couple in parallel.
I do have to go back there, so I'll see how I feel. The 'garden' is like a jungle and clipping the cable to the wall on the right all the way along it to the boundary was not a nice job!
That said, the reading is now adequate and I've no reason to suspect the 1st 8 foot of a second electrode would be any different.

A couple of pictures....

Old and new rod. I originally wondered if I was measuring the conduit and the conductor wasn't connected to the rod any more. But I got the same high reading testing the old rod. (Getting the top off was fun!)
Extending earth rods making minimal difference? 1663276839842 - EletriciansForums.net

Extending earth rods making minimal difference? 1663276886980 - EletriciansForums.net
Is it an old mining area? Maybe a sewer or old rail/smuggler's tunnel?
In general, yes, it is an old mining area, but I'm not aware of any old coal fields in this bit. I would have expected some discernible difference in effort required if I'd broken into a void of some kind. I'll probably never know the answer. It just felt very strange.
At the end of the day the reading is at least acceptable.
 

pc1966

Esteemed
Arms
Reaction score
9,863
In general, yes, it is an old mining area, but I'm not aware of any old coal fields in this bit. I would have expected some discernible difference in effort required if I'd broken into a void of some kind. I'll probably never know the answer. It just felt very strange.
At the end of the day the reading is at least acceptable.
How were you measuring it?

Just wondering if using MFT's Zs/Ze and you are now seeing the impedance of the other rod at a TT supply end limiting the performance.
 

Reply to Extending earth rods making minimal difference? in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Seems to be my month for finding odd bodges by supposed professionals. Installing an external socket in a shed today at a park home (non-mobile...
Replies
12
Views
2K
Been on a job today and debating what to put on the certificate. The DNO in early 2013 upgraded the supply and installed PME. The previous setup...
Replies
49
Views
13K
Hi, As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning. I put 8 rods in, this was one...
Replies
31
Views
3K
Deleted member 9648
D
Hi, I ordered a Fluke ES165X Earth Spike Test Kit yesterday, arrived this morning, has a go with it in the garden, popped a single 5/8 rod in and...
Replies
46
Views
4K
I was going to just add on to Voltz's thread but it seemed to come to a natural end but I had some questions. 1. A few experienced members say...
Replies
21
Views
8K
GEOFF S
G

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top