Hi
Newbie here returning to the trade after years off the tools, requalified and wondering why I bothered. I called a DNO this morning to enquire if the supply to a property was TT or TN-S as there apppeared to be a 30 year old DIY modification to the earthing arrangement. The customer was adamanet that no electrical work had been done since the place was rewired 30 years ago.
I'd upgraded the C/U to split load, dual RCD and completed all the dead tests [all radial circuits and all surprisingly good] and started Zs and got whacky results all between 12.8 AND 13.5 ohms.
Back to the basics as I looked at what I'd taken as TN-S pulled apart various earth cables to discover that a cunningly hidded earth clamp attached a cable to the armour of the incomer mascarading as the DNO earth taking a tortuous and hidden route to the MET and the cable to the earth rod left unconnected and buried in the garden!
To the point, rather than send out an engineer under flashing amber lights why couldn't they confirm the original supply details? Don't they keep records anymore? all I wanted to do was to make sure that it wasn't a poor TN-S and by the time they arrived a new rod was in and connected!
Anyway hello!
 
Last time I wanted information their records office had burnt down.
If you want information:
1/ unroll your prayer mat
2/ check the direction it's pointing in with you're pocket compass. (E)
3/ drop to you're knees and pray to Mecca!
 
Last edited by a moderator:
Why the hell didn't you ask about the possibility of a PME connection?? So what did you bung in for the new earth rod, a 1m twig?? I bet that really upped your Ze/Ra value?? lol!!
 
Why the hell didn't you ask about the possibility of a PME connection?? So what did you bung in for the new earth rod, a 1m twig?? I bet that really upped your Ze/Ra value?? lol!!

once the nice chap in the call centre had convinced me there was no chance of a record of the installation I banged in a request for PME, which quote "will be reviewed and passed to the approriate team who will attend the address to discuss the request with the home owner". I took that as "stop meddling and go and belt a lump of copper coated rubbish into the ground and fasten it to something".
 
No disrespect to any any body that works for the DNO, but I have had the misfortune of having to ring them twice

1) First time i was pricing a DB and noticed the main service fuse was missing a carrier and was exposing live parts.. i leave the scene and when i return they have sealed with tape and told the customer to wait for a letter and they will come and repair

2) Conducting a EICR, first box - Services Cut out.. C1... There was a big gaping hole in the cut out and to my discused live parts.. At first thought these things happen. When i informed the customer they were shocked as they had only had a guy out the day before changing the meter.. Why on earth would he leave it in that condition????
 
Hi
Newbie here returning to the trade after years off the tools, requalified and wondering why I bothered. I called a DNO this morning to enquire if the supply to a property was TT or TN-S as there apppeared to be a 30 year old DIY modification to the earthing arrangement. The customer was adamanet that no electrical work had been done since the place was rewired 30 years ago.
I'd upgraded the C/U to split load, dual RCD and completed all the dead tests [all radial circuits and all surprisingly good] and started Zs and got whacky results all between 12.8 AND 13.5 ohms.
Back to the basics as I looked at what I'd taken as TN-S pulled apart various earth cables to discover that a cunningly hidded earth clamp attached a cable to the armour of the incomer mascarading as the DNO earth taking a tortuous and hidden route to the MET and the cable to the earth rod left unconnected and buried in the garden!
To the point, rather than send out an engineer under flashing amber lights why couldn't they confirm the original supply details? Don't they keep records anymore? all I wanted to do was to make sure that it wasn't a poor TN-S and by the time they arrived a new rod was in and connected!
Anyway hello!
well if the mod was 30 years ago.....
then just get yoursen a Ze....(visuals first of course)..the usual (tug test n stuff)....if the external is good.....
happy days..
 
Was doing some council work on landlords CU upgrades, arranged for the dno to hook up my tails, out of the 5 jobs , 2 ended up reverse polarity. only saving grace i was energising my side after them. So i took photos , cut his seals off and pulled the bullet and swapped them around. Then my company gets a snotty letter of complaint about cutting seals off......... photos sent before during and after, resulted in no further action for some reason lol.
 
Was doing some council work on landlords CU upgrades, arranged for the dno to hook up my tails, out of the 5 jobs , 2 ended up reverse polarity. only saving grace i was energising my side after them. So i took photos , cut his seals off and pulled the bullet and swapped them around. Then my company gets a snotty letter of complaint about cutting seals off......... photos sent before during and after, resulted in no further action for some reason lol.
i hope you let slip that pics were to be retained by yoursel for `future reference`...lol...
 
look....sometimes the DNOs are a law unto themselves....time amd time again we come across poor standards by them....
but were to conform ....right?..
lol...
 
As far as i'm aware the DNO do not install meters, this work is contracted out to a meter installing company. Most of the guy's working for these companies are lucky if they get a couple of days training, ....They are NOT electricians as they used to be!! Yet another area of our Industry that has been thoroughly de-skilled and let go of, without even a whimper!!!!
 
I know that you'll all be surprised to hear this but their attendance has been. First attempt - missed the time slot given by the home owner. Second attempt - missed the time slot given by the home owner. Third booking - no show. Well it has been raining. Any takers on if they'll find the enthuisam to run in a PME? No, me neither!!!
 
I know that you'll all be surprised to hear this but their attendance has been. First attempt - missed the time slot given by the home owner. Second attempt - missed the time slot given by the home owner. Third booking - no show. Well it has been raining. Any takers on if they'll find the enthuisam to run in a PME? No, me neither!!!

If it's available at the consumers service head (eg, ....Main distribution network cable is/has been PME'd) they won't need to run anything. A 10 minute job at the service head, or about an hours work, if they change the service head at the same time to a pucker PME head!!!
 
They finally turned up yesterday. Dug a hole in the pavement and verge and left leaving the following message with my customer "tell 'im it's fixed, we tested it and it's now 0.2, OK" and left leaving the hole filling crew to arrive at some vague future point. They chose not to upgrade the head leaving the crappy one as in their words " there are worse, Missus"!
 

Reply to DNO Attendance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the...
Replies
11
Views
4K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Evening all, I’d appreciate your opinions here: I’m looking at an old (150 years+) stone house. Complete rewire and renovation. DNO fuse is...
Replies
2
Views
3K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock