Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the earthing system down as a TN-S and a ZE of 0.21. However as you can see the main earthing conductor (16mm) doesn't go to what appears to be a DNO MET, I presume it goes to an earth rod hence the Ze reading I got of 28.2 Ohms and a Zdb reading of 16.2 Ohms. All of my ELIT readings are around the 19 Ohm mark though. I did try a Ze from the DNO's block and got 30 odd Ohms so not sure what it's there for? Any Thoughts? I'm unable to lift the tiled floor in the porch to confirm if an earth rod is installed however from previous experience similar age houses in the same are are TT'd.

IMG_3957.jpeg
IMG_3956.jpeg
 
Last edited by a moderator:
sounds like a TT . never get reading that high on a TN unless there's a problem.
 
I can't seem to expand the 2nd picture which is the important one.
Also, just wondering, is there an up front RCD or RCD main switch on the consumer unit? It looks like either a dual RCD / split load board. Some people have been known to get twitchy about single insulated link cables prior to the RCD protection on a TT setup, rightly or wrongly.
 
Not too well up on the UK stuff

So doesn't look like TN anyhow from the pics , dunno why the external fault loop is 30ohm there on the DNO ? MET

As above I suppose , is there upfront RCD on the board ?
 
I can't seem to expand the 2nd picture which is the important one.
Also, just wondering, is there an up front RCD or RCD main switch on the consumer unit? It looks like either a dual RCD / split load board. Some people have been known to get twitchy about single insulated link cables prior to the RCD protection on a TT setup, rightly or wrongly.

The board was set up as a split load board with 2 Non-RCD protected lighting circuits, No Up-Front RCD, I've moved the two lighting circuits to the RCD protected side.

(The abandoned cables are for cooker and shower which are not being utilised and must be coiled or JB'd somewhere. Also the smoke detector circuit which had the CPC cut out of it for some strange reason, battery ones now installed).

The worrying this is the landlord seems to think it was rewired 12ish years ago meaning the two lighting circuits have had no RCD protection on a TT system for that length of time, the PEFC was 9 amps meaning a direct earth fault would take around half an hour to trip.
 

Attachments

  • IMG_3955.jpeg
    493.1 KB · Views: 12
I see what you mean. It looks as though it had an effective TNS setup once.
You could take a length of 2nd hand nicely faded 16mm earth, connect it in addition between that block and the CU and then call the DNO reporting a high Ze. You have evidence they supplied an earth once, and evidence it was once effective (the EICR paperwork).
Chances are it will find itself being changed to TNCS before you can say 'earth rod'.
 
So doesn't look like TN anyhow from the pics , dunno why the external fault loop is 30ohm there on the DNO ? MET

As above I suppose , is there upfront RCD on the board
there you go mikegh .
 
I'd call the DNO it's not that uncommon to find what you have found these days because an electrician CBA to call the DNO and thinks it's easier to knock an earth rod in
 
I'd try a Ze from the block below the meter, looks like a TN just never had the earth connected.
I think he did that and that is what he says is giving 30 ohms! (Can't quote top post for some reason.)

I also think the consumer unit as it stands presents an interesting conundrum regarding regs. As far as I can see it wouldn't have complied with 17th or Amendment 3 without an up front RCD due to the single insulated internal links before the RCD input terminals. Strangely it may comply with 18th in that regard as the revised reg regarding internal links specifically applies to metal consumer units. But other factors make it obvious it wasn't installed to 18th. My point being I can't see a moment in time when it was ok to install exactly that setup.
I'm weighing up whether I'd just move the tails to the top of the RCD and dispense with the main switch completely as to my thinking that would have complied once.

As above, I'd be inclined to contact the DNO saying the TNS earthing is giving a Ze of 30 ohms and the house has no visible means of providing a main earth.
 
Last edited:

Reply to Curious DNO MET on TT System in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
962

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock