shazbutz

Hi
Newbie here returning to the trade after years off the tools, requalified and wondering why I bothered. I called a DNO this morning to enquire if the supply to a property was TT or TN-S as there apppeared to be a 30 year old DIY modification to the earthing arrangement. The customer was adamanet that no electrical work had been done since the place was rewired 30 years ago.
I'd upgraded the C/U to split load, dual RCD and completed all the dead tests [all radial circuits and all surprisingly good] and started Zs and got whacky results all between 12.8 AND 13.5 ohms.
Back to the basics as I looked at what I'd taken as TN-S pulled apart various earth cables to discover that a cunningly hidded earth clamp attached a cable to the armour of the incomer mascarading as the DNO earth taking a tortuous and hidden route to the MET and the cable to the earth rod left unconnected and buried in the garden!
To the point, rather than send out an engineer under flashing amber lights why couldn't they confirm the original supply details? Don't they keep records anymore? all I wanted to do was to make sure that it wasn't a poor TN-S and by the time they arrived a new rod was in and connected!
Anyway hello!
 
Last time I wanted information their records office had burnt down.
If you want information:
1/ unroll your prayer mat
2/ check the direction it's pointing in with you're pocket compass. (E)
3/ drop to you're knees and pray to Mecca!
 
Last edited by a moderator:
Why the hell didn't you ask about the possibility of a PME connection?? So what did you bung in for the new earth rod, a 1m twig?? I bet that really upped your Ze/Ra value?? lol!!
 
Why the hell didn't you ask about the possibility of a PME connection?? So what did you bung in for the new earth rod, a 1m twig?? I bet that really upped your Ze/Ra value?? lol!!

once the nice chap in the call centre had convinced me there was no chance of a record of the installation I banged in a request for PME, which quote "will be reviewed and passed to the approriate team who will attend the address to discuss the request with the home owner". I took that as "stop meddling and go and belt a lump of copper coated rubbish into the ground and fasten it to something".
 
No disrespect to any any body that works for the DNO, but I have had the misfortune of having to ring them twice

1) First time i was pricing a DB and noticed the main service fuse was missing a carrier and was exposing live parts.. i leave the scene and when i return they have sealed with tape and told the customer to wait for a letter and they will come and repair

2) Conducting a EICR, first box - Services Cut out.. C1... There was a big gaping hole in the cut out and to my discused live parts.. At first thought these things happen. When i informed the customer they were shocked as they had only had a guy out the day before changing the meter.. Why on earth would he leave it in that condition????
 
Hi
Newbie here returning to the trade after years off the tools, requalified and wondering why I bothered. I called a DNO this morning to enquire if the supply to a property was TT or TN-S as there apppeared to be a 30 year old DIY modification to the earthing arrangement. The customer was adamanet that no electrical work had been done since the place was rewired 30 years ago.
I'd upgraded the C/U to split load, dual RCD and completed all the dead tests [all radial circuits and all surprisingly good] and started Zs and got whacky results all between 12.8 AND 13.5 ohms.
Back to the basics as I looked at what I'd taken as TN-S pulled apart various earth cables to discover that a cunningly hidded earth clamp attached a cable to the armour of the incomer mascarading as the DNO earth taking a tortuous and hidden route to the MET and the cable to the earth rod left unconnected and buried in the garden!
To the point, rather than send out an engineer under flashing amber lights why couldn't they confirm the original supply details? Don't they keep records anymore? all I wanted to do was to make sure that it wasn't a poor TN-S and by the time they arrived a new rod was in and connected!
Anyway hello!
well if the mod was 30 years ago.....
then just get yoursen a Ze....(visuals first of course)..the usual (tug test n stuff)....if the external is good.....
happy days..
 

Reply to DNO Attendance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I've recently had 2 customers enquire about installing a backup generator for their domestic premises. After a lot of research...
Replies
17
Views
3K
Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the...
Replies
11
Views
4K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
I have come across what I think is a looped supply - like a normal incomer but two of them coming up side by side. It's a TN-S arrangement with an...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock