Whilst I appreciate your replies, I'm not sure my questions have been answered. Let's say the current rod ra is 60 ohms, Do I need to fit another? If so, should this be independent of the current one?
 
There are more than enough Threads on this subject here on the forum, check them out!!

But the last thing you want on any TT system is a ridiculously high 100/200 ohm Ra value, where your totally relying on a single unreliable RCD device for your earth fault protection covering several circuits. Just because it states a figure of 200 ohms in BS 7671, DOESN'T mean that's the figure you aim for, or should be happy with.... Oh, and never use those thin short 3/8'' twigs (so-called rods) you will never achieve anything like a suitable or stable value....

See post 24 of this thread praising an Ra of 15 ohms..........http://www.electriciansforums.co.uk...cal-forum/77449-tt-installing-5-8-rods-2.html

"Nothing more needs to be said than ...Well Done!! Though for the life of me, with all those power tools you say that you own, .....Why didn't you use a decent SDS hammer to drive them rods in?? A few minutes and you'd of been done and wouldn't leave a bloody big entry hole from all the swinging around of the rod!! lol!!"

Cant possibly be relying on one of those nasty o'll RCD's though can it?
 
Whilst I appreciate your replies, I'm not sure my questions have been answered. Let's say the current rod ra is 60 ohms, Do I need to fit another? If so, should this be independent of the current one?

my input is: take the TT earth through the SWA and bang in a decent extra rod. how to you think DNO get TNC-S values of < 0.35---- by rodding all the way down the line.
 
A new earth rod should be installed in each outbuilding . They may well be linked together which will give you parallel earth paths thus lowering the Ra . Hope this makes things clear. Each outbuilding should have its own earth zone because if the main earth is lost at the mains u will still have a reliable earth in the outbuilding .
 
he'll not get a reliable earth with a 3ft. coathanger. big rods, drivven deep is the only way.
 
There are plenty of issues with exporting PME.

Where are you planning on exporting it to anyway? France?
 
Enlighten you about what? I believe engineer 54 has already said all that is necessary on the subject in this thread already.
 
Did that already..... no problem extending pme.
You made a statement and i wanted to know the issues with extending pme????
 
There are no issues with extending PME, I don't recall having said that there are. You haven't asked what the issues are with extending PME either
 
JEEEEZZ!
You said there are plenty of issues with exporting pme and i said enlighten me{ what are the issues is all im asking} SIMPLES
 