dazza1981
Thanks mdj
Thanks mdj
How to you think DNO get TNC-S values of < 0.35---- by rodding all the way down the line.
Nope - its primarily because the Neutral is connected to Earth at the sub-station!
Nope - its primarily because the Neutral is connected to Earth at the sub-station!
I recently have done a similar installation to an out building. I installed a new submain to the building with a new DB and earthing stake. I used a 16mm 3 core SWA but did not connect the 3 core (used as earth) to the house earth, therefore keeping it seperate but still protecting the submain via a 3rd core and the steel armour. Also my Ra reading was 60ohms after installing 2 stakes coupled, so as stated in earlier posts, depth is good!
See post 24 of this thread praising an Ra of 15 ohms..........http://www.electriciansforums.co.uk...cal-forum/77449-tt-installing-5-8-rods-2.html
"Nothing more needs to be said than ...Well Done!! Though for the life of me, with all those power tools you say that you own, .....Why didn't you use a decent SDS hammer to drive them rods in?? A few minutes and you'd of been done and wouldn't leave a bloody big entry hole from all the swinging around of the rod!! lol!!"
Cant possibly be relying on one of those nasty o'll RCD's though can it?
Should the sub-main cable not have had its earth connected to the appropriate earth for the associated OCPD though rather than the new earth you have created at its load end?