Engineer54
So.......a second earth stake has to be fitted. BUT, should this be independent of the original??
A second earth rod position at the new building is the correct way to go, linking the two rod positions either with a 3rd core or the armouring of the supply SWA cable!! It is totally pointless to have 2 independant TT systems on a single installation!! Can't make it any clearer than that for you.