Correct access is the issue here I would much rather run one cable from the other side of house then work from sub bard rater than potentially 8 cables. Plus would only help with volt drops and achieve better Zs readings
 
Correct access is the issue here I would much rather run one cable from the other side of house then work from sub bard rater than potentially 8 cables. Plus would only help with volt drops and achieve better Zs readings
If I was to just extend circuits then ring circuit would have 30 x double sockets, this to me is very bad practice. I would like to do the job properly and have the circuits split up into reasonable sizes. The last thing I want is something like the original part of the house having a problem, tripping RCBO and then being called because extension sockets not working. COme on who wants their whole house socket outlets covered by one circuit. Same goes for lighting circuits​




Where are you getting 8 cables from?? I thought we were talking about a lounge and a couple of bedrooms one with an en suite??

You say if you extended the original ring you'll end-up with 30 outlets, are you saying this house has currently only one ring circuit for up and downstairs?? ...And one lighting circuit if you're saying that the same applies to the lighting as well...

There are very few circumstances where a remote separate CU is actually warranted in a typical sized house that's being extended. Remote CU's are normally installed in such circumstances, where it benefits the electrician rather than the installation or the customer!!​
 
yep Mike...although if buried under the floor surface then as its strictly speaking not visible would require additional protection by means of RCD top end...
go for the 10mm 3 core SWA for this....

have to disagree with you there, glenn. 522.6.101 refers to cables buried in walls, not under floors. in that case they would have to be > 50mm deep anyway.
 
16mm sub mains !!??
for an additional load that will barely exceed 12A by my reckoning ??
doesnt matter how many frigging sockets your adding , bedrooms hardly pull more than 6A each under normal use.
**** me , you'd think domestic work was rocket science reading this thread
 
Where are you getting 8 cables from?? I thought we were talking about a lounge and a couple of bedrooms one with an en suite??

You say if you extended the original ring you'll end-up with 30 outlets, are you saying this house has currently only one ring circuit for up and downstairs?? ...And one lighting circuit if you're saying that the same applies to the lighting as well...

There are very few circumstances where a remote separate CU is actually warranted in a typical sized house that's being extended. Remote CU's are normally installed in such circumstances, where it benefits the electrician rather than the installation or the customer!![/INDENT]

There is currently only one floor which is served by one ring, same for lighting.
 
have to disagree with you there, glenn. 522.6.101 refers to cables buried in walls, not under floors. in that case they would have to be > 50mm deep anyway.
but i`m looking at it from the point of view of penetration by nails, screws & the like...this applies to scant walls....and as i see it also to floors where the unskilled/uninstructed bla bla bla...
 
So it's not a house, it's a bungalow at the moment?? So is it being converted to a house now, or just converting the loft into a bedroom and extending the lounge and a bedroom. To me, this is even less of a reason to start installing sepaate CU's
 

OFFICIAL SPONSORS

Back
Top