Have you programmed it by way of the usb port.
 
Have you programmed it using their software. What was the problem with the Twinflex panel you replaced.
Why haven't you connected the cpcs to the appropriate terminals.
 
Last edited:
Have you programmed it by way of the usb port.
[/QUOT
It is replacement penal I do not how to programme ,I tried to follow its manual. but I cant get it right.
Have you programmed it using their software. What was the problem with the Twinflex panel you replaced.
[/QUOT
no I did not use software as I had couple of suggestion which recommended I do not need to use sofware
Have you programmed it using their software. What was the problem with the Twinflex panel you replaced.
Why haven't you connected the cpcs to the appropriate terminals.
i have been suggested there is no need to use software.
Basically I do now how to program it.the old was faulty and it was showing EOL missing,I am not competent but I am an Elecrition trainee ,I thought there is no need to put cpcs in appropriate terminals as old one was in connector blocks so I did same.
Thanks again for your help
 
i have been suggested there is no need to use software.
Basically I do now how to program it.the old was faulty and it was showing EOL missing,I am not competent but I am an Elecrition trainee ,I thought there is no need to put cpcs in appropriate terminals as old one was in connector blocks so I did same.
Thanks again for your help


CPCs should always be correctly connected, just because someone previously didn't and created a dangerous situation it does not mean that you should copy them.
 
I would suggest you contact a fire alarm company, hold your hands up and tell them you need help.
 

Reply to Fike zone faults in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock