Hi guys,

How easy is it to ad 5 smokes & 1 call point to a conventional alarm system?

Cheers,

Paul
 
easy. first find out if you have an unused zone. if so, use it for your new additions. if not, you have 2 options with an existing zone. either:

1. find the end detector and daisy chain from there, moving the eol device to the new end of line.

or:

2. pick a convenient detector and divert the radial through your new detectors then back to the existing detector.

as long as you have a radial with no spurs off.
 
Yeah that bit i get, im just not sure if theres anything i should be doing because its seems that easy?
 
it's as easy as fitting a lighting radial without switch drops.
 
fit diode bases if the call point is after the smokes.other than that the hardest thing is pulling the cable in
 
I was going to take a new leg out from the board because the end of line is miles away an then come back to board after looping all the smokes and pick up and join the old leg
 
as long as it ends up as a straight radial, no spurs/branches.
 
I was going to take a new leg out from the board because the end of line is miles away an then come back to board after looping all the smokes and pick up and join the old leg

it could be cheaper and quicker to upgrade the panel for the additional zones,you can get a decent panel for £150,
 
Im doing a similar thing,sorry to hijack your post,adding 1 detector to an existing zone which is wired in grey twin(not fp200)its a domestic property(private house),im not sure that if your adding new cable that it should be fp200 or not.
 
I cant AM, im on a budget an the companys quite tight on money at the mo & watching what their spending out on. Anything else i should no when i reinstall the supply? Also what is the maximum number of points you can have to one zone, say on a 100m of cable?
 
Im doing a similar thing,sorry to hijack your post,adding 1 detector to an existing zone which is wired in grey twin(not fp200)its a domestic property(private house),im not sure that if your adding new cable that it should be fp200 or not.

if its a new zone use fp,if its adding to a zone with t&e using fp with add no real benefit
 
depends on the panel. manufacturers advice is best advice here.
 
I cant AM, im on a budget an the companys quite tight on money at the mo & watching what their spending out on. Anything else i should no when i reinstall the supply? Also what is the maximum number of points you can have to one zone, say on a 100m of cable?
i cant see the logic in not spending £150 to make the job quicker,it will be cheaper than the rate to install a cable hours wise the customer gets a new panel for free so they think saves you money on the install...20 devices per zone
 
AM, just to digress. it's standard practice to use red FP200, but is it obligatory? reason i ask is that i'm in the middle of an install and i'm about 30m short of cable, but i do have some white FP200, rather than having to buy 100m red,
 
AM, just to digress. it's standard practice to use red FP200, but is it obligatory? reason i ask is that i'm in the middle of an install and i'm about 30m short of cable, but i do have some white FP200, rather than having to buy 100m red,

not sure on that to be honest,never give it a thought if its fire rated its fire rated,id use it..
 
Wiring the additional points is the easy part have you thought about re-commisioning and certifying these additions.
 
Another quick couple questions ( ive don nout on theses things ) can the smoke heads go on a slight angle because the stairwell ceiling is about 45o and is it also ok to join fp in a galv through box? Oh and one other thing, once ive finished is it as easy as turning the power back on and everything should be ready to go? Cheers guy
 
Another quick couple questions ( ive don nout on theses things ) can the smoke heads go on a slight angle because the stairwell ceiling is about 45o and is it also ok to join fp in a galv through box? Oh and one other thing, once ive finished is it as easy as turning the power back on and everything should be ready to go? Cheers guy

yes,yes and yes..but after power up smoke all the heads youve fitted to test them
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Fire alarm help please....asap
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
Paul Chick,
Last reply from
Paul Chick,
Replies
25
Views
2,180

Advert

Back
Top