ricardo123
When I try and zero my fluke 1652 leads they are giving me a high reading so when I do an R1+R2 test the results come back as zero. Messing up my other readings as well like Zs, Ze test etc. I think they originally zero'd out to about 0.08 now I am getting around 0.6 - 0.8 ohms.
I tried giving the crocodile teeth a little clean but no change.
Anyone come across this before!?
I tried giving the crocodile teeth a little clean but no change.
Anyone come across this before!?
. The manufacturers standard method is by way of the Fluke zero adaptor (provided as part of all 15xxB series kits), a fancy piece of bent metal with 4mm sockets, which enables any combination of leads to zeroed reliably, even the BS1363 loop/RCD test lead. A scrap piece of 30mm wide x 50mm long copper busbar with 3 x 4mm holes in one end for nulling the 3 lead set or shorting the pins of the BS1363 plug. Alternatively 300 mm length of 1mmsq CPC wrapped round the pins of the BS1363 plug of the loop/RCD test lead are reasonable substitutes. Another method used by one of my colleges is to short the BS1363 pins on a stainless steel drainer, but it's a bit bulky to carry with you
. The particularly important point is giving the croc-clips something to bite on and a method that doesn't require juggling all the leads at once.