hhhunzai
With 3MΏ at 415 V I’d be inclined to just switch it back in to service. If it holds then OK, if it blows you will have a better (lower) fault reading. You really can’t do fault finding of this type with a multi meter. As to the Wheatstone bridge 3MΏ is to high for it to work.
As you have suggested to switch it back, It was already working but sometimes it makes problems, either due to moisture or or any thing else.
there were two cables with same ratings and cores, one is working with showing infinity resistance and the other is showing 2 to 3M ohms.
I have,t checked with a Megger or cable tester.
You make me understand about Wheatstone method I will try to figure it out by myself.