monoloco

Apologies if this isn't the appropriate bit of the forum to post this to, or for any uneducated comments in what follows - straying beyond my elec expertise!

We had our meter changed over to a digital one the other day & the guy who did it spotted we had an old fused neutral cut-out. So Western Power Distribution have been out today wanting to replace it.

I understand enough to appreciate it needs replacing (not that I'd personally be fiddling with wires to come a cropper if the neutral fuse did get blown), but they're saying they need to dig up w nice hole/trench in our (recently tarmaced) driveway to fix it.

Is there a good reason why the service head couldn't safely be replaced without doing that, or is it genuinely unavoidable?

I just want to make sure they're not doing the thing that's easiest/cheapest for them, but not best for us!

Thanks!
 
The swapping of your cut out should not involve digging anything up. You should phone them and find out exactly why they need to dig it up and post back what they tell you.
 
I'm not sure either - they didn't explain to my wife.

How would they usually isolate it to swap the head (or is that not necessary)?
 
Only reasons I can think of is to extend the service cable to facilitate the head change, or t repair a section of damaged cable identified on the survey.
Whatever the reason, we can only guess, and as Dillb says only the DNO can answer this.
 
Some of the old cutouts are in a very poor state, and have lots of earth metal that can't be made earth free. The only way to work on it safely is to cut off the supply, hence hole in drive or road.
 
Thanks all.

I'll give them a call and report back.

If it helps to see the cut-out then here's a picture of the offending item!

image.jpg
 
There are ways of doing it BUT to do it safely there isn’t. The DNO’s are obliged to change these heads, at one time they’d modify them.

Post a picture on something like photo bucket and link it to here. If there’s sufficient length on the incomer it can be done, near the floor, forget it.

Do you really appreciate why the neutral shouldn’t be fused?

Pity you only put UK as your location. Some systems were originally DC and converted to AC at a later date. I’m particularly interested in these systems as I’ve lived in two houses that were originally DC. One +ve the other –ve, they were next door to each other.
 
Thanks Tony. Is that photo I've posted visible?

There's only a couple of inches more of the incomer exposed below what you can see there.

As for whether I really appreciate why the neutral shouldn't be fused - as I suggested, this definitely ain't my specialist subject, but I get that the fuse could blow and leave you not realising the circuit's still hot.

Can you explain how it's help to know my location? We're in Gloucestershire - a 1930's house.
 
That cut-out looks very similar to those fitted on 1930's properties,where,on occasion,the DNO or their agents do fit a joint in preference to working on an old unit.

On my own 1937 property,they renewed the head,no problems,in about an hour,but my pal,on the same road,had a joint put in,about a meter from the cut-out.

I inspected his cut-out, previous to this work,and it looked no worse than mine. I think a lot depends on the crew that turn up,and what mood they are in,as when i mentioned this to the lads that did mine,they told me the other crew must "sit down to have a wee"...(actual quote) :jester:
 
It goes without saying that you must not in any way attempt to even open that cutout, let alone do anything else to it.
But for anyone who is interested here's a few pages from the book.
ImageUploadedByTapatalk1429571983.118688.jpg
ImageUploadedByTapatalk1429572028.975680.jpg
And if you are wondering what tools the modern cable jointer might require to practise his trade, here's the list.
ImageUploadedByTapatalk1429572262.906013.jpg
ImageUploadedByTapatalk1429572283.521294.jpg
 