Hi all, happy Christmas! There was a thread on this subject a while back, not many people said that they actually connect bathroom extractor via a 3A fuse, despite many MI's seemingly asking for it. And certainly it's not something you see often, triple pole isolators yes, sfs's less so. Is it something we mostly just 'overlook'.
And if you were to do it, would you loop power in/out throught a sfs, then drop down to light switch off load side. All bath lights and fan off load side? Do away with TP iso?
 
I emailed Manrose about this a couple of months ago, to see if the switched live to the fan needed fusing down as well as the permanent live. Perhaps I didn't word the question very well, as I got an ambiguous reply.

Me:
Hi,
The MF100T instructions require that a 3A fuse is fitted. Does this need to be fitted so that it protects the permanent live, the switched live, or further upstream so that it protects both?
Thanks,
Pretty Mouth

Reply:
Hi Pretty Mouth,
Hope you are well,
The 3A fuse would be fitted early on in the installation on the permanent live,
Hope this helps.
 
I emailed Manrose about this a couple of months ago, to see if the switched live to the fan needed fusing down as well as the permanent live. Perhaps I didn't word the question very well, as I got an ambiguous reply.

Me:
Hi,
The MF100T instructions require that a 3A fuse is fitted. Does this need to be fitted so that it protects the permanent live, the switched live, or further upstream so that it protects both?
Thanks,
Pretty Mouth

Reply:
Hi Pretty Mouth,
Hope you are well,
The 3A fuse would be fitted early on in the installation on the permanent live,
Hope this helps.
Have started using Greenwood Airvac fans and the ventaxia inline fans which don,t need a 3A fuse as long as cct has a 6A mcb.
Can make life easier.
Regards,S
 
If required, like @Baddegg , I will fuse down the whole of the bathroom to ensure both permanent live and switched live are covered. If the manufacturers instructions state it should be fused (or show it in their wiring diagrams) I would follow this guidance... the regs state quite clearly manufacturers instructions should be taken into account and I'm not sure I have the technical knowledge to argue the case in court should it come down to it.

That being said, I'm moving to fitting fans that don't require it such as the S&P fans but I give the client the option with a brief run down of the costs associated with both approaches. The S&P fans aren't cheap but when you compare it to parts and labour to modify the circuit (assuming you can get to it easily enough to make that job relatively quick) in the short term at least it's far more appealing from a price perspective to use a more expensive fan that doesn't require a fusedown.
 
Is that correct? Surely a sfs would serve this purpose? Is the idea of a triple pole iso for maintenance from a particular regulation?

A triple pole isolator isolates all live conductors - neutral, live, switched live.
 

Reply to Fusing bathroom timer fans in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top