Just been to speak to him, the man charged him £230 for the work.

He asked for a cert so he is dropping one around in the morning??

Also I looked again in the electric cupboard where the meter is and the 100a isolator, it looks like he has cut the main Earth coming from the western power supply and put it in a connector block, then taken a new 10mm earth to the 100a isolator so he has an earth there for his 2.5 twin and earth cable to supply the shed. I've read that the main Earth can't be cut and should be continuous??
 
Just been to speak to him, the man charged him £230 for the work.

He asked for a cert so he is dropping one around in the morning??

Also I looked again in the electric cupboard where the meter is and the 100a isolator, it looks like he has cut the main Earth coming from the western power supply and put it in a connector block, then taken a new 10mm earth to the 100a isolator so he has an earth there for his 2.5 twin and earth cable to supply the shed. I've read that the main Earth can't be cut and should be continuous??

The MET can be positioned as you describe, but post a picture for clarity
 
IMG_7581.JPG
IMG_7582.JPG
IMG_7588.JPG
 
Good pictures, but think Murdoch said it all in 2 small words.

No seals on the service head ?

So he's cut the Earth and used an ordinary connector wrapped in tape ?.
 
Last edited by a moderator:
Yeah it looks like he has done that. I'm not even sure if he has used a connector block, I haven't touched it to take the tape off!

Does the main incoming earth need to be continuous? With no joints etc
 
What's with the red tape on the Live outgoing conductor? also ruined the IP rating of the isolator.
 
The warning notice did a lot of good. Get your mate to get a competent electrician in, even if it's just to disconnect that mess.

PS; the 'tails' to the CU look a bit suspect as well. Nicely fashioned hole for them as well.
 
@Jacko If he was going to cut into the Earth like that, he should have used a proper block to make the connection. But with the way everything else has been done, it's only to be expected.
That 2.5 has no protection at all, so in the event of a fault the cable may well fry.
There's no RCD protection so in the event of someone touching something that has become live, basically they're going to get Electrocuted. (Read as: Likely DEAD).

One of the boys asked where he'd left his horse, to be honest I wouldn't insult Cowboy's by calling him one.
 
Last edited by a moderator: