6mm t + e from db (32a breaker) going to a garage unit. is this right?
 
M

Mike P

  • Thread Starter Thread Starter
  • #2
Provided it's protected and it is on an RCD either in garage or main cons unit, should be O.K. I would run a 6mm earth with it as well. distance is relative check earth loop.
 
W

wannabesparky

  • Thread Starter Thread Starter
  • #3
Provided it's protected and it is on an RCD either in garage or main cons unit, should be O.K. I would run a 6mm earth with it as well. distance is relative check earth loop.

thankyou
 
I would consider running the supply cable in SWA rather than T&E. Also it should be RCD protected at the consumer unit so that the whole circuit is RCD protected. I would also consider the earthing arrangements, as if it is a TNCS (PME) supply, then it is not permitted to take a PME earth outside the main building unless the earth CSA is the same size as the main earth conductor.

I would also do a full cable calc and determine what is going to be used in the garage as this may have a bearing on the supply cable size as will the installation method of the supply cable, ie buried in the ground etc
 