Provided it's protected and it is on an RCD either in garage or main cons unit, should be O.K. I would run a 6mm earth with it as well. distance is relative check earth loop.
 
I would consider running the supply cable in SWA rather than T&E. Also it should be RCD protected at the consumer unit so that the whole circuit is RCD protected. I would also consider the earthing arrangements, as if it is a TNCS (PME) supply, then it is not permitted to take a PME earth outside the main building unless the earth CSA is the same size as the main earth conductor.

I would also do a full cable calc and determine what is going to be used in the garage as this may have a bearing on the supply cable size as will the installation method of the supply cable, ie buried in the ground etc
 
Last edited:

Reply to garage unit in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock