Sl1210

the only reason I can think you may need a contactor ( not contractor!) would be if you wished to switch all heaters on or off together, from one point, with one switch.

this switch, marked "heating" would engage the contactor that would in turn supply the heaters ( various mcbs and circuits as per Biffs comment).
 
i'm not re-wiring the place just modifying a few things. its a pain because most of the flat is on 1 ring. i have used one of the existing radiala to feed the 2 plate hob. and run another radial to supply the cooker. i'm going to use the old 6mm cooker circuit to feed the boiler. the rest is pretty much on the ring.

i have a feeling the heaters may be switch on together as she showed me a thermostat and some sort of controller as i was leaving, so more then likely that is what the contactor is for.
 
turns out the board that was supplied with the contactor and mcb's was solely just for the four heaters so they can all be turned on via a digital programmer and a thermostat so each heater will need a radial run to it via a switch spur from the 16a mcb's at the board.
 