Hi, I am looking for advice on protecting generator fed circuits. When the genny starts to run out of fuel it spits and farts and sends the voltage all over the place. What I want to do is disconnect the circuits before any thing gets damaged by over voltage. its a small 3kva single phase standby genny feeding a small workshop, they get the occasional power cut and want to keep things running, I have fitted a manual change over switch and they switch that over and start the genny by hand. Just switching everything off when they notice the genny running out of fuel is not an option.
Any advice welcome, thanks
 
You may be cheaper to get an auto change over switch with this protection built in , than make it your self .
Even then on the genny you have mentioned , I would be surprised if it ran any where near a constant output even if all was well !?
I am sure E54 will respond to this one at some point and give a more comprehensive post .



Edit; I am sure you could configure a G59 relay to do what you want , but they probably cost more as a stand alone unit than the whole package from a genny supplier ?
 
Last edited:
Depends on what equipment this generator is supplying, but personally i wouldn't entertain any generator without the provision of an AVR, supplying anything more than typical site lighting and hand tools and the like....

Without an AVR, the voltage is governed by speed which in turn is directly proportional to the load being drawn....
 