Hey everyone.
I have the stuff to backfeed my generator through a 30amp breaker. I have the lockout kit that prevents both the breaker and main from being on at the same time. My question is this: My generator is strong enough to run a 50 amp and a 30 amp cord at the same time. Can I backfeed them both into the box at the same time? I would like to power all of my house and think it would if this is possible. I am not sure the 30 amp alone will do everything. The generator is 7500 running watts. I'll list my appliances needed to run below.
Navien tankless boiler for heat (2- pumps and three thermostats)
3/4hp water pump (well water)
Small chest freezer
Refrigerator
Double element water heater
Single element water heater
House lights (all led bulbs)

Extras:
Wi-fi, TV, Cable box, microwave, propane stove (electric lock)

Let me know what you think
 
Break out the schematics for your generator at look what size the main breaker on it is, just because it has a 50 amp plug on it doesn't mean it's 50 amps nor will they actually put out 50 amps! As a matter of fact on most of the higher wattage portable generators the main breaker on them is only 35 amps, just because they have 50 amp plugs on them don't mean squat! Any generator that puts out over 30 amps is going to have a 50 amp plug on it, dont let yourself think that means your generator will actually put out 50 amps just because it has a 50 amp plug on it.
 
Last edited:
As a matter of fact here is the schematics of my Wen11000, it puts out 11000 starting watts and 8300 running watts yet the main breaker on it is only a double pole 35 amp like on most others that size, I use it to backfeed my panel when the power is out using an 8awg cable fed to a 35amp breaker in the panel that that's controlled by a manual interlock preventing it from feeding my panel unless the main breaker is off ..........
 

Attachments

  • Wen11000Schematic.jpg
    Wen11000Schematic.jpg
    243.1 KB · Views: 39
Last edited:
As a matter of fact here is the schematics of my Wen11000, it puts out 11000 starting watts and 8300 running watts yet the main breaker on it is only a double pole 35 amp like on most others that size, I use it to backfeed my panel when the power is out using an 8awg cable fed to a 35amp breaker in the panel that that's controlled by a manual interlock preventing it from feeding my panel unless the main breaker is off ..........
As a matter of fact here is the schematics of my Wen11000, it puts out 11000 starting watts and 8300 running watts yet the main breaker on it is only a double pole 35 amp like on most others that size, I use it to backfeed my panel when the power is out using an 8awg cable fed to a 35amp breaker in the panel that that's controlled by a manual interlock preventing it from feeding my panel unless the main breaker is off ..........

Came across your post searching for which to use. I’m running the WEN11000 and am trying to set up a manual transfer switch by (reliance) to my house. Even though it says 50 and 30amp on the generator, would you recommend using a 30 amp transfer switch or the 50amp. I’m confused on if I have to use the 50 because of the higher watts the generator puts out. Think 30amp switches rate for 7200-8k. Overloading either is a non issue as I’ll be only using a few things but I want to get the most out of the generator for the home for future use. What are your thoughts?
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Perry, MI
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Generator to breaker box 30 amp and 50 amp
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
dreidel13,
Last reply from
Megawatt,
Replies
18
Views
21,774

Advert

Back
Top