Doing an EICR today and had an odd, lower than expected, resistance reading on a ring final CPC.

r1 = 0.21Ω
rn = 0.21Ω
r2 = 0.18Ω
R1+R2 = 0.09Ω

I was expecting around the 0.35Ω for the CPC but was quite surprised to see the reading I got.

As this was the supply to a kitchen ring I could see and access all 7 2g sockets (property is empty but tenants were moving in later today) and the 2 switched fused spurs for the washing machine and under counter fridge. So I took all the fronts off and checked all terminations were correct.

The only thing I can surmise is that there is a parallel earth path somewhere on the circuit, but I couldn't see where. Nothing was ran in any conduit that I could see and all the cable entry points had normal grommets. I noted it in the comments section of the report anyway for future reference.

But wondered if anyone else had ever had that happen before? I never have and rang my CPS technical helpline to check and they agreed it is most likely a parallel earth path somewhere. Unless some of you more knowledgeable lot have any other suggestions?
 
Parralell paths came to mind as i was reading Prior to your mention Of this.

Kitchen ring so boiler could be supplementary bonded. Possibly the pipe work in kitchen is bonded.

possibly a couple of hard wired or even just plugged in appliances connected to water pipes.
 
Also seen it for gas cooker / hob where the ignition system is on FCU or plugged in and of course metal gas pipes bonded.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Shropshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Had a weird CPC reading today
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Raptor0014,
Last reply from
pc1966,
Replies
2
Views
2,130

Advert