hello I did an EICR today on a flat probably about 10 years old. everything fine except the usual C3s for non rcd protected circuits and for plastic boards etc. my question is has anyone come across the type of cable I found going from 80mcb near cut out to con unit in the flat. at first I thought it was 3 core 4mm swa until I open up the con-unit. Ive been sparking since 2004 and aint ever seen this type of cable.

the brown core is 16mm
there are 7 x 2.5mm blue cores whichs equates to 17.5mm
and theres 4 x 2.5mm bare cores resulting in 10mm

The submain does disappear in to wall so I wanna know if I just treat this like I would of if it was 16mm twin and earth sub main and put c3 down for not rcd protection to cable

this is the first time I have ever posted anything on here so if I'm doing anything wrong please let me know
 

Attachments

  • cores1.png
    770.1 KB · Views: 68
  • cores close up.png
    343.6 KB · Views: 68
Those neutral and earth bars are inadequate to terminate those conductors. They should be in the same terminal, the earthing conductor would only appear to have two strands terminated.
 
That is split concentric cable, no it does not satisfy the requirement for an earthed metallic screen or armour as most of the concentric conductor is connected to neutral, not earth.

Plus of course there's the other obvious issues in the pictures that need to be coded.
 
Out of interest, where is this sitting in relation to the meter? Reason for asking is because if it's actually part of a Building Network (so, what could be construed as DNO) then I believe it's a bit of a grey area as to what is the relevant applicable standard. Either way it's a dog's dinner, and that's probably an insult to the chef too!
 
Split concentric cable, but is prohibited in this application.

I don't know what the earthing arrangement is, but it's tn-s, tn-c-s, or tt.

Since the earth is re-combined with the neutral (and then split at the cu ) the system has become

Tn-s-c-s
Tn-c-s-c-s
Or tt-nc-s

All of which are prohibited!

If the split-con cable was used on the tn-c incomer and finally split to tn-c-s once then it would be valid, however usually only the dno can do this, sort of different if it's a private transformer
 
Split concentric cable, but is prohibited in this application.

I don't know what the earthing arrangement is, but it's tn-s, tn-c-s, or tt.

Since the earth is re-combined with the neutral (and then split at the cu ) the system has become

Tn-s-c-s
Tn-c-s-c-s
Or tt-nc-s

All of which are prohibited!

If the split-con cable was used on the tn-c incomer and finally split to tn-c-s once then it would be valid, however usually only the dno can do this, sort of different if it's a private transformer
say what?! Slowwwwly.....
 
say what?! Slowwwwly.....
At the incomer the cores have been split to L, N, and earth - you can see the three cables coming in.

This split concentric cable joins the N and E together - which is prohibited (joined quite well or fairly poorly depending on which outer wires are used at each end).

In effect this additional combining of pen gives the silly earthing arrangements
 
Last edited:
The split concentric cable joins the N and E together - which is prohibited (joined quite well or fairly poorly depending on which outer wires are used at each end).

No it doesn't, it keeps the N and E seperate, that's why it is called split concentric, the outer concentric conductor is split into two different conductors.
[automerge]1598035435[/automerge]
Only in certain installations, but not the way this has been done

By which rules and what installations?
 
No it doesn't, it keeps the N and E seperate, that's why it is called split concentric, the outer concentric conductor is split into two different conductors.
[automerge]1598035435[/automerge]


By which rules and what installations?
Yes, but usually they are separately identified - these don't look to do so - it could be that only one set of outer wires goes to neutral, and the other to earth, but as I see that particular instance such segregation isn't guaranteed, it looks like a random selection of outer wires split between n&e rather than proper split.

The neutral wires usually have continuous insulation, it looks to me that its sleeved - on my phone anyway
 
Yes, but usually they are separately identified - these don't look to do so - it could be that only one set of outer wires goes to neutral, and the other to earth, but as I see that particular instance such segregation isn't guaranteed, it looks like a random selection of outer wires split between n&e rather than proper split.

The neutral wires usually have continuous insulation, it looks to me that its sleeved - on my phone anyway

They are seperately identified, the blue cores insulated cores are connected to the neutral bar and the bare earth cores have been sleeved and connected to the earth bar.
 
They are seperately identified, the blue cores insulated cores are connected to the neutral bar and the bare earth cores have been sleeved and connected to the earth bar.
Perhaps it is me and my phone, but it looks like sleeving on both n&e to me, if not and it's been done correctly then I stand corrected.
 

Reply to Has anyone come across this type of cable for a submain. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
699
I get how they work and can kind of understand the reasoning, I remember the early "no-trip" RCD testers, D-LOG made one that saturated the RCD...
Replies
11
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
745
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
677
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock