Discuss Have come across a 16A Ring Final in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I would chanlenge you on that As many consider primary benefit of RFC to be secondary earthing (or connection route) should the cable gets disconnection or damage along the route.
While I am not a fan of RFC myself another of the benefits greater then its maximum fuse size is that in the event of lose or limited connection the other leg will have lower resistance and as such the resulted arcing is likely to be far lower to none, where on radial where there is no parallel path all current would have have to flow through it.
Dunno

Id say its hard to argue that capacity is the main benefit

'Secondary earthing' , lower efli and volt drop would be Secondary benefits I reckon
 
I always thought the old 32a RFC was to save cable and so that an entire houses sockets could be wired in 1 big circuit.
This was when you probably only had 7 maybe 8 sockets in an entire 3 bedroom property.
Many old houses you work on often still have the old 3036 board with just 3 circuits , Lights , Ring and Cooker
 
I always thought the old 32a RFC was to save cable and so that an entire houses sockets could be wired in 1 big circuit.
This was when you probably only had 7 maybe 8 sockets in an entire 3 bedroom property.
Many old houses you work on often still have the old 3036 board with just 3 circuits , Lights , Ring and Cooker
They'd be related wouldn't they

Material costs and capacity

2 sides of the same coin I reckon
 
There are two limits to length of cable in ring finals, one is enough current should be able to flow to operate the magnetic part of the MCB/RCBO and the other is the voltage should not drop below the limits.

The latter is rather hit and miss, there is no hard and fast rules, we are told it is worked out as 20 amp in centre as 12 amp even spread, so 26 amp is used to calculate cable length and with 2.5 mm that works out at 106 meters.

But with a large home, by dropping to 16 amp you can have 180 meters of cable, personally would look at lollipop idea and use even 10 mm if required to a twin cooker outlet plate and form the ring final from that. But there is no hard and fast rules, I have in the past used 6 mm to junction boxes and spurs to each socket in a warehouse where the 24 foot drops from false ceiling in the refrigerated room would have cause problems with volt drop for the cleaning equipment to be used in the cheese store.

Although designed for homes, ring finals are used elsewhere, but in the home the advantage is reduction of cable used, and number of RCBO's required to allow many sockets which can have the 3 kW load without causing it to trip.

In the main swapping to less than 32 amp is because of an error somewhere.
 
Has the circuit been down rated due to the installation of the cable running through thermal insulation? I've seen a couple like this where a large amount of cellotex insulation was used!
Sy
 

Reply to Have come across a 16A Ring Final in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
789
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Have come accross a job where house ring run in T/E but has an old extension with earthed metal conduit used for sockets and only live and neutral...
Replies
6
Views
1K
Hi there all, I have a property and I have noticed the following wiring (please see below) in one of the rooms in the house. It looks like the...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock