Jrhuling

Hello!
I have a 320 amp service (400 amps) in a main panel. I want to create a subpanel 1,000 feet away with a 200 amp service there. Can someone tell me what size wires to run, if aluminum or copper, and how many wires? For, say a 3% voltage drop? How would you do it?

Thank you!
 
Hello!
I have a 320 amp service (400 amps) in a main panel. I want to create a subpanel 1,000 feet away with a 200 amp service there. Can someone tell me what size wires to run, if aluminum or copper, and how many wires? For, say a 3% voltage drop? How would you do it?

Thank you!
Employ someone that is competent. to do the install and design for you
 
I will be employing someone to help. But I don't need to be up-charged for the materials. Thats why I would like to find out what folks recommend for cable sizing.
The site, the incoming supply characteristics, the cable run and the distribution requirements will need assessing by a professional electrician to determine what type and size of cable is required. This will be an expensive run of cable and should be designed properly.
 
I will be employing someone to help. But I don't need to be up-charged for the materials. Thats why I would like to find out what folks recommend for cable sizing.
No spark is going to use bigger cable than necessary.
 
Hello!
I have a 320 amp service (400 amps) in a main panel. I want to create a subpanel 1,000 feet away with a 200 amp service there. Can someone tell me what size wires to run, if aluminum or copper, and how many wires? For, say a 3% voltage drop? How would you do it?

Thank you!
I’ll tell you # 3/0 copper to each panel. You will need 2 # 3/0 for your hots, one 3/0 for your neutral and one # 6 ground
 