Jumping on this thread rather than starting another. Ive been asked to change a landlord's board, that supply's a block of flats. The supply to each flat is in twin and earth. The flats consumer units have rcd protection so if I make the circuits on the landlord board rcbo they're as likely to trip if there's a problem in a flat. Other than rewire the supply to each flat in swa (which they won't go for). What are my options?

Don't think there is one. Unless the T&E is surface or conduit all the way then it will need 30mA RCD protection
 
Other than rewire the supply to each flat in swa (which they won't go for). What are my options?
The critical issue here is if there is any sub-main cables buried at less than 50mm from the surface. If you can establish there is not that risk, then supplies from fuses (like a Ryefield board) or MCCB/MCB become a reasonable solution.

Otherwise the only compliant solution is 30mA RCD (or RCBO) protection and that is likely to have nuisance trip issues due to the total leakage of the flats, as well as very poor selectivity.
 
Will have to look and see if I can trace where the cables run. Can't see them going for the work if requires running in new feeds so will be left on mcb's anyway
 