Hi all,

I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.

House is almost certainly post 60's. CPC's present in lighting circuit.

Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.

So there is some sort of reading.

Loose connection?

Back tomorrow so any advice on where to start always appreciated.

It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.

Like I said - where to start.

There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
 
Hi all,

I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.

House is almost certainly post 60's. CPC's present in lighting circuit.

Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.

So there is some sort of reading.

Loose connection?

Back tomorrow so any advice on where to start always appreciated.

It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.

Like I said - where to start.

There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
What was your MFT set on?
 
I would do a R1 +R2 at other lights on the circuit.

In a house of that age CPC's may be present, but they may not have been connected up.....
 
I would do a R1 +R2 at other lights on the circuit.

In a house of that age CPC's may be present, but they may not have been connected up.....
Yep, link at CU and test at the lighting points first.
Although, are you saying the lives are looped at the switches and neutrals at lights? If so, switch 'em on first:rolleyes:
 
I have found an older (red an black) 1mm twin and earth cable with the earth discontinuous in part of the run. Either a manufacturing defect or the 1mm pulled too hard during installation I reckon, as the cable appeared ok externally.
 
I have found an older (red an black) 1mm twin and earth cable with the earth discontinuous in part of the run. Either a manufacturing defect or the 1mm pulled too hard during installation I reckon, as the cable appeared ok externally.

And this is exactly why I tell apprentices to check for continuity at EVERY point/accessory. You never know if the cable inside the sheath is continuous or has snapped and pulled a part!!

Jay
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
High R2 - Lighting Circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
52
Unsolved
--

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
Marcus Vaughan,
Replies
52
Views
5,068

Advert

Back
Top