Marcus Vaughan

-
Esteemed
Reaction score
240
Hi all,

I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.

House is almost certainly post 60's. CPC's present in lighting circuit.

Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.

So there is some sort of reading.

Loose connection?

Back tomorrow so any advice on where to start always appreciated.

It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.

Like I said - where to start.

There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
 
Hi all,

I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.

House is almost certainly post 60's. CPC's present in lighting circuit.

Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.

So there is some sort of reading.

Loose connection?

Back tomorrow so any advice on where to start always appreciated.

It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.

Like I said - where to start.

There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
What was your MFT set on?
 
I would do a R1 +R2 at other lights on the circuit.

In a house of that age CPC's may be present, but they may not have been connected up.....
 
I would do a R1 +R2 at other lights on the circuit.

In a house of that age CPC's may be present, but they may not have been connected up.....
Yep, link at CU and test at the lighting points first.
Although, are you saying the lives are looped at the switches and neutrals at lights? If so, switch 'em on first:rolleyes:
 
I have found an older (red an black) 1mm twin and earth cable with the earth discontinuous in part of the run. Either a manufacturing defect or the 1mm pulled too hard during installation I reckon, as the cable appeared ok externally.
 
I have found an older (red an black) 1mm twin and earth cable with the earth discontinuous in part of the run. Either a manufacturing defect or the 1mm pulled too hard during installation I reckon, as the cable appeared ok externally.

And this is exactly why I tell apprentices to check for continuity at EVERY point/accessory. You never know if the cable inside the sheath is continuous or has snapped and pulled a part!!

Jay
 
Does the home owner have the certificate for the installation of the CU? The schedule of test results could make interesting reading

I’ll ask. I was thinking that because I was getting 50k ohms rather that complete open circuit that the install designed to be earthed but something has gone wrong somewhere. I have already sorted out a couple of tapped up connections outside of enclosures - that sort of thing.
 
the reading you are getting could be a return path via the filament of a bulb and the neutral.

You need to do proper dead tests........
 
Take lamps out, take L, N,&E of the circuit out of C.U join live and earth at C.U. do R1 +R2 from there back through circuit probably loose/poor connected earth.
 
If you take lamps out and you haven't got any loads between live and neutral you may not need to it just rules out rouge results.
 
And it’s probably a 100 downlighters!

Turn off all the light switches & do the R1 + R2 with both live and neutral disconnected from the CU - obviously you need to turn the switch on at the light you are working on..

You've mentioned singles - are the CPC's singles or is the set up reliant on the conduit for the earth continuity?
 
upload_2018-1-17_13-53-14.png
now that came to mind !
 
Thanks All. Sure enough CPC was present at consumer unit in with the line. It reached two out of the 8 rooms in the circuit.

Found no less than 4 disconnect CPC’s at junction boxes. I managed to clear the faults to switches at least and a couple of pendants. Never got round to the downlighters - that’s a can if worms. Pretty sure all the CPC faults were caused by whoever riddled the ceiling with the downlighters. Very poor installation.

The customer grumbled about the fault finding though stated ‘I want everything safe for insurance purposes’ but wasn’t prepared to pay for it. I basically worked for an extra 3 hours for free.

Perhaps if the fault was on the line or neutral they would be more understanding?

Thanks all. I can close this ‘Minor Works’ out.

I had a issue with the RCD testing though - all three failed.....new thread.

F7C1870A-BC42-4408-A99D-83F4AAECD9BB.jpeg


7D39F8CD-BB8A-4B5E-AAC8-4943357F1AD5.jpeg
 
The customer grumbled about the fault finding though stated ‘I want everything safe for insurance purposes’ but wasn’t prepared to pay for it. I basically worked for an extra 3 hours for free.
I would have walked away from that job. before I start a job I tell the customer
if you want a job doing I tell them no earths on lighting circuits, right down to the bonding the job will not be done .
 
View attachment 40297now that came to mind !
I would have walked away from that job. before I start a job I tell the customer
if you want a job doing I tell them no earths on lighting circuits, right down to the bonding the job will not be done .

I think I must be a soft touch. I take a conscientious approach and always do loads of little extras ‘I’ll just tidy that up so they have no further problems’

I need to toughen up.

I’m a . (Supposed to be a -----!)

Today was a school day in so many ways.
 

Reply to High R2 - Lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
730
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of...
Replies
2
Views
839

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock