Farmelectrics

-
Arms
Reaction score
520
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on lighting circuit 22 ohms, fused spur for heater 21 ohms so I thought maybe its a tt system but when I tested sockets I got a reading of 0.69 ohms ze at cabin db was 22 ohms so why the lower reading for the sockets
 
if I'm honest not sure was told it was a tns but need to confirm on Monday weve only landed a site hut on site and was asked to provide a test cert for the cabin
 
agree Essex i did do the ze and pscc pfc first that's were i got the 22 ohm reading from the lighting circuit was similar as was the spur at this stage i wasn't concerned as i presumed it must be a tt system but when i carried out a zs on ring main i got 0.69 and am simply asking why
 
Did you retest the lighting circuit once you got a reduced Zs on the ring final circuit.
 
agree Essex i did do the ze and pscc pfc first that's were i got the 22 ohm reading from the lighting circuit was similar as was the spur at this stage i wasn't concerned as i presumed it must be a tt system but when i carried out a zs on ring main i got 0.69 and am simply asking why

Where did you test the Ze? It should have been clear what the earthing arrangement is it that point.
 
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on lighting circuit 22 ohms, fused spur for heater 21 ohms so I thought maybe its a tt system but when I tested sockets I got a reading of 0.69 ohms ze at cabin db was 22 ohms so why the lower reading for the sockets
Neutral/Earth fault on sockets.
 
there are no faults on sockets dead tests were all ok I took a zs at the site cabin sorry not a ze now I know the cabins are protected by a commando socket / rcd so the readings are actually ok ie 1667 ohms but its the zs of 0.69 that had me scratching my head will retest on Monday but was looking for ideas on the matter thanks in advance
 
It is possible the external impedance of the cabin dramatically changed between tests. You need to work back to the source and confirm the earthing system before you continue.
 
just wondering if an operator error took a reading L-N instead of L-E?????
 

Reply to high zs readings on site cabin in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock