I've got some Legrand dimmer modues, 7354-46.
They are rated at 300w but with the setup that I have I'd really like to use one of them on a circuit with a load of 420w.
I've read before that MK dimmers can handle 200% of their rated load.
Anyone know how much these Legrand dimmers can handle before you're really to risk causing damage?
 
i would not even attempt to overrun any dimmer. in my experience, most struggle to cope with their rated load, let alone an overload.
 
I would say if states 300W then that should be the largest load you put through the switch, whether there is a tolerance or not.

If the manufacturer was confident in their device at 200% then they would rate it at that wattage surely?
 
I can't lie in any more, I always wake up at 7am or earlier, but to be honest this is the only time I get to myself these days. Until the wife and my boy emerge I can do whatever I want, it's so cool man. Apparently it's inappropriate to start drinking at this time though. Shame. ;)
 
Fitted a dimmer (400W) 3.5 year ago - got asked to replace as busted - it was controlling (happily) a 200w halogen light. This had popped and the nugget had put a 500w one in.

I agree with above posts re: handling rated loads they seem fragile at best.
 
I've got some Legrand dimmer modues, 7354-46.
They are rated at 300w but with the setup that I have I'd really like to use one of them on a circuit with a load of 420w.
I've read before that MK dimmers can handle 200% of their rated load.
Anyone know how much these Legrand dimmers can handle before you're really to risk causing damage?

75% of the rated value
 
Dimmer modules like those mentioned when co-located in grids usually need de-rating sometimes to 30% of the rated wattage depending on how many dimmer modules are fitted in the grid.

From past experience dimmers rarely last when run close to their maximum ratings and I can only think the 200% mentioned would possibly be a short term rating to cope with inrush when turned on and / or the brief peaks caused by lamp failure.
 
Down rating depends on load type. Always down rate by power factor of load, so 75% is a good starting point ( if dimmer can handle this type of load at all). Obviously not applicable for resistive load
I think Philips dimmable LEDs state to down rate by around 90 %ie 30w load on a 300w dimmer.
 
What ever happened to the reg's and following manufacturers guidelines you are only asking for trouble - heat dissipation is a major issue with dimmers and do often incur derating factors when grouped ... the hypothetical 200% you may have heard may be a short term loading tolerance before damage occurs and not continuous operational loading. Its similar to the KVA rating on say a 110v transformer these are actually in some cases misleading as its not a continuous load rating but a short term value... it is common to find a much lower KVA continuous rating in the instructions or on the plate but ironically tey advertise for the higher value of which they can't maintain.
 
The load that I wanted to put through the dimmer was 420w, which I thought might have been ok as manufacturer's ratings tend to err on the side of caution, wishful thinking perhaps.
The common consensus doesn't recommend this so I decided to play it safe and went with a 240w max load.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
How many watts can a 300w rated Legrand dimmer really handle?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
scania164,
Last reply from
telectrix,
Replies
17
Views
3,101

Advert

Back
Top