Hi, I have just had a full rewire done on my house by a Napit registered company whom I didn't realise at the time where allowing none registered persons to do the work. I have had to call them back several times to many issues I came across and am now concerned about the safety of the rewire. I have a couple of pictures that they say are not a problem, but I am just not sure!
I would really appreciate it if somebody would have a quick look at the pictures and tell me if they look to be ok?

The first picture is showing the cables twisted around each other under the floor boards (they were also the same in the walls), the other pictures are of six cables going into a dimmer and a double switch that are next to each other, the dimmer is for the bathroom light and the double switch is for the loft light and inline extractor fan in the loft. The final picture is of a dimmer in the kitchen.

Thank you
 

Attachments

  • I need a professional opinion on a recent rewire please wire 1.JPG - EletriciansForums.net
    wire 1.JPG
    156.1 KB · Views: 153
  • I need a professional opinion on a recent rewire please 397928c0-6c65-4eee-b20e-45a18f0897db.JPG - EletriciansForums.net
    397928c0-6c65-4eee-b20e-45a18f0897db.JPG
    93.8 KB · Views: 150
  • I need a professional opinion on a recent rewire please 6921495a-ae87-426f-88fa-92acb026f7e2.JPG - EletriciansForums.net
    6921495a-ae87-426f-88fa-92acb026f7e2.JPG
    103.1 KB · Views: 148
  • I need a professional opinion on a recent rewire please 0cf1638b-9fd7-4366-b334-12dff5ed8099 2.JPG - EletriciansForums.net
    0cf1638b-9fd7-4366-b334-12dff5ed8099 2.JPG
    185.2 KB · Views: 145
  • I need a professional opinion on a recent rewire please 5e1faaf9-9eb8-4554-99bc-e96b6cc7e543 2.JPG - EletriciansForums.net
    5e1faaf9-9eb8-4554-99bc-e96b6cc7e543 2.JPG
    120.6 KB · Views: 146
  • I need a professional opinion on a recent rewire please 46fecc84-9bbb-45f9-ad99-4a5202696225 2.JPG - EletriciansForums.net
    46fecc84-9bbb-45f9-ad99-4a5202696225 2.JPG
    248.5 KB · Views: 142
  • I need a professional opinion on a recent rewire please 8471a7c7-9adb-4c17-a540-e68d7d727cd8 2.JPG - EletriciansForums.net
    8471a7c7-9adb-4c17-a540-e68d7d727cd8 2.JPG
    171.7 KB · Views: 142
  • I need a professional opinion on a recent rewire please 37907d46-8b44-4e66-9d5c-632e13cd78f9 2.JPG - EletriciansForums.net
    37907d46-8b44-4e66-9d5c-632e13cd78f9 2.JPG
    140.1 KB · Views: 141
  • I need a professional opinion on a recent rewire please 6921495a-ae87-426f-88fa-92acb026f7e2.JPG - EletriciansForums.net
    6921495a-ae87-426f-88fa-92acb026f7e2.JPG
    103.1 KB · Views: 145
  • I need a professional opinion on a recent rewire please 0871d4a2-cc3d-4b6c-8af3-196ec3d10853.JPG - EletriciansForums.net
    0871d4a2-cc3d-4b6c-8af3-196ec3d10853.JPG
    236.1 KB · Views: 145
Theres too much copper showing and sheaths not brought into enclosures

I don't work in UK but I've never heard of any rules on cables twisted like that ,.doubt there is anything
 
Last edited:
Just looks like a lazy spark, it’s as if he couldn’t be bothered, now you’ve looked the switches but what are the parts like that you can’t see, I would contact napit and tell them your not happy with the condition of the installation
 
I think you proding around in there has made things a lot worse if you’re that concerned get a eicr instead of messing yourself no questions it dosnt look great but you have definitely made things worse
 
It looks like several accessories are not earthed correctly or have a CPC (earth) connected to them. I would recommend putting your concerns in writing to the contractor and also send a copy to NAPIT, allow them the chance to rectify any concerns you have.

If they're not forthcoming or carry out the work satisfactorily I would commission and independent electrician to carry out a periodic inspection of their work and raise a report on their findings, then I would contact NAPIT to let them sort it out.

They've taken a lot of short cuts just in those pictures, I'd hate to think what's been hidden away.
 
It looks like several accessories are not earthed correctly or have a CPC (earth) connected to them. I would recommend putting your concerns in writing to the contractor and also send a copy to NAPIT, allow them the chance to rectify any concerns you have.

If they're not forthcoming or carry out the work satisfactorily I would commission and independent electrician to carry out a periodic inspection of their work and raise a report on their findings, then I would contact NAPIT to let them sort it out.

They've taken a lot of short cuts just in those pictures, I'd hate to think what's been hidden away.
Hi, thanks very much for your reply.
He has been back out several times and I am still finding issues.
It's what I can't see as you say, that I'm now concerned about.

Thanks for your advice
 
I'm not sure what half the pics are trying to show but to me it looks OK from a safety point of view but it's just rough as a badger's.

They grommeted the metal back box and have sleeved the earths, so that's something. It's just that there are some fittings without sheathing going into the box like they should and the second fixing on the wires is shoddy, far too much copper showing.

Don't think this is necessarily inherently dangerous since i've seen a million properties like this but it's just rough. I wouldn't be concerned about your house burning down or anything though.

EDIT: Missed metal not being earthed. That needs to be sorted - if the right fault appears someone could get a belt off that.

Make sure they put RCD protection in at the board.
 
I think you proding around in there has made things a lot worse if you’re that concerned get a eicr instead of messing yourself no questions it dosnt look great but you have definitely made things worse
Thanks for reply but I have not touched anything. I just unscrewed the faceplates to see if I could straighten them because they they are miles out, and then took pictures
 

Reply to I need a professional opinion on a recent rewire please in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock