This is too good an opportunity to check my understanding of the adiabatic equation.

Type B breaker

I = 5 x 32A = 160A
t = 0.1
k = 115
S = minimum csa

S = SQR(I² x t) ÷ k

50.6 ÷ 115 = 0.44 mm²

Therefore 1mm² is good to go.
the value for I is incorrect mate. You need to measure the zs of the circuit, to work out the actual fault current. Higher reading the better! In your situation
 
Not quite.

You need to calculate the ACTUAL disconnection time with the ACTUAL fault current at that point. Typically a BS EN 60898 circuit breaker has an instantaneous operating time quoted as 0.1 seconds, however if you consult the manufacturer's data then there may be a definite minimum operating time of around 0.01 seconds at your value of prospective fault current at the extremity of the circuit. This could help achieve a smaller cpc csa.

Then so long as the result, i.e. S, is no greater than the cpc cross-sectional area that you have then it is adequate. This is an iterative calculation, so when designing you would have to recalculate as you increase the cpc csa as this will affect the Zs and prospective earth fault current, which will subsequently affect the size of cpc given as the minimum (i.e. it will increase - so you need to ensure that your new csa is adequate after calculation).

I agree about using the actual prospective earth fault current.

However, shouldn't it be the PEFC at the origin of the circuit? After all, the fault might occur at the nearest socket to the origin, or even in the cable before the first socket.

You might have to refer to the manufacturer's spec for I²t let-through energy and put that figure into the adiabatic equation instead of separate figures for I and t to arrive at a sensible answer.
 
However, shouldn't it be the PEFC at the origin of the circuit? After all, the fault might occur at the nearest socket to the origin, or even in the cable before the first socket.

No, because the worst case will be with the slowest disconnection time (i.e. at the extremity of the circuit). The lower prospective current at that point will cause the longest disconnection time which will thermally stress the conductors more.

In reality it can be advisable to carry out the calculation for both near end and far end faults to find the worst case, although it is generally assumed to be far end.
 
No, because the worst case will be with the slowest disconnection time (i.e. at the extremity of the circuit). The lower prospective current at that point will cause the longest disconnection time which will thermally stress the conductors more.

In reality it can be advisable to carry out the calculation for both near end and far end faults to find the worst case, although it is generally assumed to be far end.

Looks like I need to try plugging in a few figures and see how it works out.
 
Thanks guys. Juggling figures is easy! knowing what figures to juggle is the essence and this forum undoubtedly helps me understand.
I'm going back to the job this afternoon to perform the relevant tests.
I'll also look up manufacturer's specifications and respond later too.
 

Reply to Identifying csa of t&e in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock