zap

-
Reaction score
65
Greetings.
I tested an rfc and recorded the following results:
r1 = 0.62
rN = 0.89
r2 = 1.45
The difference in r1 and rN indicate loose connections so I checked all the sockets (bar one) on the ring which revealed two loose connections.
The rfc now tests as follows:
r1 = 0.58
rN = 0.59
r2 = 1.45
The measurements indicate a 80 metre circuit of 2.5mm^2 csa.
I've checked every socket in the dwelling except one which feeds a waterbed and is inaccessible. So I told the customer that I have some homework to do before I can issue certification.
BUT, I hadn't realised that it could be 2.5/1 t&e in which case the measurement of 1.45 (remaining constant) is correct.
I don't have a micrometer to measure the cpc so how do I confirm the cable conductor's csa? ... and if it's 1mm^2 cpc is that okay?

The wiring is about 25 - 30 years old.
 
what you could try is connect L to E on one side of the ring and leave the other open at the board, check the R1 R2 readings at the sockets nearest then move further along until you notice any major jump , if its a gradual increase on all then o/k ,
 
what you could try is connect L to E on one side of the ring and leave the other open at the board, check the R1 R2 readings at the sockets nearest then move further along until you notice any major jump , if its a gradual increase on all then o/k ,
to make this quicker, wire a plug with a bit of flex from it going to connector strip.

this makes it quick to a quick check without removing fronts (very useful if there if there is a dead short somewhere)

or if you have a multimeter etc with non gs38 leads just shove them in the socket
 
Thanks, R G,
The route the cable takes is not obvious but I sort of did what you're suggesting with expected results.
If the cpc is 1mm^2 is it acceptable (i.e. compliant with BS767)?
 
I would compare a bit of new cable with the old , for the earth wire size , if you have test leads to a plug then you won't need to remove the socket fronts ...

If you have done this then as shanky says if Zs is good at end of circuit then its o/k
 
I would compare a bit of new cable with the old , for the earth wire size , if you have test leads to a socket then you won't need to remove the socket fronts ...

Thanks again R G,
I started to doubt myself and stopped thinking clearly.

Is it satisfactory to have a 1mm cpc on a rfc protected by a 32A type b breaker?
 
What were your test results?

Preliminary result was too high i.e. 1.45 Ohms. But two loose connections have been rectified since so I'm returning to retest and this time I expect satisfactory results.

Thanks again for helping me understand.
 
1.omm cpc is acceptable provided that you calculate the min. size of cpc from the pefc, using the adiabatic equation and the trip time of the ocpd. ( usually 0.1 sec. with a k value of 115).
 
1.omm cpc is acceptable provided that you calculate the min. size of cpc from the pefc, using the adiabatic equation and the trip time of the ocpd. ( usually 0.1 sec. with a k value of 115).

This is too good an opportunity to check my understanding of the adiabatic equation.

Type B breaker

I = 5 x 32A = 160A
t = 0.1
k = 115
S = minimum csa

S = SQR(I² x t) ÷ k

50.6 ÷ 115 = 0.44 mm²

Therefore 1mm² is good to go.
 
Last edited:
Not quite.

You need to calculate the ACTUAL disconnection time with the ACTUAL fault current at that point. Typically a BS EN 60898 circuit breaker has an instantaneous operating time quoted as 0.1 seconds, however if you consult the manufacturer's data then there may be a definite minimum operating time of around 0.01 seconds at your value of prospective fault current at the extremity of the circuit. This could help achieve a smaller cpc csa.

Then so long as the result, i.e. S, is no greater than the cpc cross-sectional area that you have then it is adequate. This is an iterative calculation, so when designing you would have to recalculate as you increase the cpc csa as this will affect the Zs and prospective earth fault current, which will subsequently affect the size of cpc given as the minimum (i.e. it will increase - so you need to ensure that your new csa is adequate after calculation).
 
Thanks again R G,
I started to doubt myself and stopped thinking clearly.

Is it satisfactory to have a 1mm cpc on a rfc protected by a 32A type b breaker?

Sometimes it is and other times it isn't. Just calculate it using the adiabatic equation the same as you do for the cpc of all the circuits you install.
 
This is too good an opportunity to check my understanding of the adiabatic equation.

Type B breaker

I = 5 x 32A = 160A
t = 0.1
k = 115
S = minimum csa

S = SQR(I² x t) ÷ k

50.6 ÷ 115 = 0.44 mm²

Therefore 1mm² is good to go.
the value for I is incorrect mate. You need to measure the zs of the circuit, to work out the actual fault current. Higher reading the better! In your situation
 
Not quite.

You need to calculate the ACTUAL disconnection time with the ACTUAL fault current at that point. Typically a BS EN 60898 circuit breaker has an instantaneous operating time quoted as 0.1 seconds, however if you consult the manufacturer's data then there may be a definite minimum operating time of around 0.01 seconds at your value of prospective fault current at the extremity of the circuit. This could help achieve a smaller cpc csa.

Then so long as the result, i.e. S, is no greater than the cpc cross-sectional area that you have then it is adequate. This is an iterative calculation, so when designing you would have to recalculate as you increase the cpc csa as this will affect the Zs and prospective earth fault current, which will subsequently affect the size of cpc given as the minimum (i.e. it will increase - so you need to ensure that your new csa is adequate after calculation).

I agree about using the actual prospective earth fault current.

However, shouldn't it be the PEFC at the origin of the circuit? After all, the fault might occur at the nearest socket to the origin, or even in the cable before the first socket.

You might have to refer to the manufacturer's spec for I²t let-through energy and put that figure into the adiabatic equation instead of separate figures for I and t to arrive at a sensible answer.
 
However, shouldn't it be the PEFC at the origin of the circuit? After all, the fault might occur at the nearest socket to the origin, or even in the cable before the first socket.

No, because the worst case will be with the slowest disconnection time (i.e. at the extremity of the circuit). The lower prospective current at that point will cause the longest disconnection time which will thermally stress the conductors more.

In reality it can be advisable to carry out the calculation for both near end and far end faults to find the worst case, although it is generally assumed to be far end.
 
No, because the worst case will be with the slowest disconnection time (i.e. at the extremity of the circuit). The lower prospective current at that point will cause the longest disconnection time which will thermally stress the conductors more.

In reality it can be advisable to carry out the calculation for both near end and far end faults to find the worst case, although it is generally assumed to be far end.

Looks like I need to try plugging in a few figures and see how it works out.
 
Thanks guys. Juggling figures is easy! knowing what figures to juggle is the essence and this forum undoubtedly helps me understand.
I'm going back to the job this afternoon to perform the relevant tests.
I'll also look up manufacturer's specifications and respond later too.
 

Reply to Identifying csa of t&e in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
849

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock