I tested an rfc and recorded the following results:
r1 = 0.62
rN = 0.89
r2 = 1.45
The difference in r1 and rN indicate loose connections so I checked all the sockets (bar one) on the ring which revealed two loose connections.
The rfc now tests as follows:
r1 = 0.58
rN = 0.59
r2 = 1.45
The measurements indicate a 80 metre circuit of 2.5mm^2 csa.
I've checked every socket in the dwelling except one which feeds a waterbed and is inaccessible. So I told the customer that I have some homework to do before I can issue certification.
BUT, I hadn't realised that it could be 2.5/1 t&e in which case the measurement of 1.45 (remaining constant) is correct.
I don't have a micrometer to measure the cpc so how do I confirm the cable conductor's csa? ... and if it's 1mm^2 cpc is that okay?
The wiring is about 25 - 30 years old.
r1 = 0.62
rN = 0.89
r2 = 1.45
r1 = 0.58
rN = 0.59
r2 = 1.45