brixtonia

-
DIY
Reaction score
3
I have a 4kW immersion heater in a thermalstore - very recently replaced by a plumber as the previous one was leaking. Supplied with a cotherm thermostat and a second pocket for a safety cutout into which the safety cutout from the previous immersion was fitted and seems to be working fine.

I smelled burning and removed the cover to find that the insulation on the wire between the cutout and the stat was melting. The end closest to the stat was clearly more affected. The stat has deformed around the point the wire connects to it and the stat has ceased to work.

The wire between the safety and the stat is exactly the same as the wire from the spur to the immersion which has been in place since I can remember. The connection seemed sound but hard to tell now.

One thing I had noticed after it was installed is that it was cycling on and off quite rapidly.

Just a faulty stat?
 
Usually, the electric immersion heater is rated at 3kW. You mention the IH is now rated at 4kW after it was replaced by the plumber. This would be something to clarify first.

A 4kW IH draws more electric current - about 16Amps - whereas a 3kW one draws about 12Amp. It is important that the cabling, connections, thermostats , switches and supply from the consumer unit are suitably rated for the power of the IH.

If you send me details of the thermal store I will look up the power of the IH which should be fitted.
 
Thank you. It has replaced a 4kw immersion and the stat is / was 20A rated. I've replaced the stat and it does not cycle in the same way. I think it must have been a fault with the stat.
 
I have a 4kW immersion heater in a thermalstore - very recently replaced by a plumber as the previous one was leaking. Supplied with a cotherm thermostat and a second pocket for a safety cutout into which the safety cutout from the previous immersion was fitted and seems to be working fine.

I smelled burning and removed the cover to find that the insulation on the wire between the cutout and the stat was melting. The end closest to the stat was clearly more affected. The stat has deformed around the point the wire connects to it and the stat has ceased to work.

The wire between the safety and the stat is exactly the same as the wire from the spur to the immersion which has been in place since I can remember. The connection seemed sound but hard to tell now.

One thing I had noticed after it was installed is that it was cycling on and off quite rapidly.

Just a faulty stat?
You can get clamp meter for a about £25 online.
 
So the new stat has also burned out. The live connects first to the safety cutout, then into the 20A temp control stat, then to the element (using 2.5mm wire). It's always the wire between the two stats which seems to overheat. The wire insulation melts and the terminal melts at the point at which it connects to the second stat (20A temp control).

The 4kw immersion element seems fine with resistance testing at about 14-15ohms. The immersion replaces another 4kw immersion.

Any suggestions?
 
Have you checked the voltage, also suggest (when repaired) check voltage drop between two above mentioned terminals.
Thanks. I will check when I have a new stat. Just noticed that the safety cutout (in line before the variable temp stat) is 16A rated. It operates fine and has been in there for years, but could its rating possibly be causing a problem for the stat?
 
I don't think so as its not doing any switching normally, your measured 14 ohm resistance means a current flow of 16.43A at a nominal 230V (if that's the UK voltage), normally, heat damage with fairly high loads is caused by lose connections but I think that is very unlikely, now at any rate, I would measure the volt drop (immersion on) between the furthest away terminals first, if no volt drop then problem elsewhere, maybe the control stat is rubbish and causing very high resistances while switching (unlikely) but if you get a volt drop of say 5V then this will result in ~ 80W heat being generated somewhere between the two stats, you can then narrow it down by probing separately across each set of stat terminals, you say it's the wire between the two stats that's overheating which might point to a control stat problem but see what readings you come up with.
 
I don't think so as its not doing any switching normally, your measured 14 ohm resistance means a current flow of 16.43A at a nominal 230V (if that's the UK voltage), normally, heat damage with fairly high loads is caused by lose connections but I think that is very unlikely, now at any rate, I would measure the volt drop (immersion on) between the furthest away terminals first, if no volt drop then problem elsewhere, maybe the control stat is rubbish and causing very high resistances while switching (unlikely) but if you get a volt drop of say 5V then this will result in ~ 80W heat being generated somewhere between the two stats, you can then narrow it down by probing separately across each set of stat terminals, you say it's the wire between the two stats that's overheating which might point to a control stat problem but see what readings you come up with.
Thanks. I will try all of this once I get a new stat. Only doubt I have about it being a faulty stat is that this has been a consistent problem with various stats. Even on the previous immersion. But then what else could it be? I don't suppose there is any mileage in changing the order of the cutout and the temp stat? Or even putting the cutout after the element?
 
Post some pictures please which includes details of the burned out link wire and its terminals.

Did you make up the link wire? If you did what did you use?

Also send a picture or details of the IH element, control stat and safety stat.

The cotherm stats I have looked up are rated at 16A which is suitable for a 3kW IH element but unsuitable for a 4kW element. Are you sure the two stats are rated at 20A?
 
Last edited:
Post some pictures please which includes details of the burned out link wire and its terminals.

Did you make up the link wire? If you did what did you use?

Also send a picture or details of the IH element, control stat and safety stat.

The cotherm stats I have looked up are rated at 16A which is suitable for a 3kW IH element but unsuitable for a 4kW element. Are you sure the two stats are rated at 20A?
The link wire is the positive wire taken from a new section of 3 core 2.5mm2.

The stats I have used are Cotherm TSD 00706 and TSD01106 - both rated 20A (and printed on the side) and, importantly, variable to 80C (as this is a Thermalstore).

The safety is a Sunvic VKL 2352 with manual reset (16A). It's been in place for a while but seems to work fine.

Can't get a photo just now and it's dismantled but as previously described mains live runs into Sunvic, then into Cotherm, then to immersion terminal. Neutral fixes to the opposite terminal. Contacts are good.
 
No switching sound but when measured with a multi meter at ambient temperature it shows no circuit up to about 60C then about 3 Ohms resistance.
Don't think that means alot because if the closed contacts of the thermostat had a resistance then they would be generating ~ 550watts in the stat itself when wired in series with the 14 ohm element.
 
Is there a reason why the tank is fitted with a 4kW element rather than the typical 3kW element? Could you use a 3kW element instead or are you in a hurry to heat up the tank?

20A rated safety and control stats such as those Cotherm types are on their limits to switch and pass 20A for long periods of time and will inevitably deteriorate through concentrated electrical heating of their contacts and connections. The physics of electrical heating is that it is proportional to the current squared not simply the value of the current. This means Ohmic heating as it is sometimes called rises rapidly with each increment of current eg (read as I/Isquared) 1/1, 2/4, 3/9, 4/16...16/256....20/400.

Those 4 kW elements require much more robust stats rated at say 30A - 40A to give reliable service. For 4kW and higher elements , ordinary stats like the cotherm ones you have are used to switch an electromagnetic switch called a contactor on and off. The stats only then have to handle the very small current required to power the contactor's electromagnetic operating coil; the contactor has substantial switch contacts and surfaces to safely and reliably close and open the immersion heater circuit through which flows 4000/230 = 17 Amps. In the early stages of heating cold water the current is likely higher than 17A because the element's resistance is lower than at warmer water temperatures.

One also needs to employ the correct power cable to the element which has heat resistant insulation suited to higher operating temperatures. It is sold as 'immersion heater cable'. eg:

Doncaster Cables Immersion Heater Cable 3183TQ 2.5mm2 x 1m Coil - https://www.travisperkins.co.uk/cable-lengths/doncaster-cables-immersion-heater-cable-3183tq-2-5mm2-x-1m-coil/p/759014

Finally the terminations of the flex must be made using ferrules or ring crimps to maximise conductivity of electricity.

I believe then the combination of 4kW IH element and those Cotherm stats is unsuitable. One could stick with the Cotherm stats if you swapped to a 3kW element. To use a 4kW element you require a 30-40A contactor.

I have not looked up your profile but if you are not an electrician then this is a job for one to complete for you. Hope this helps.
 
Last edited:
Still and all, the measured element resistance is 14 ohms or 16.43A at 230V, so, is it really outrageous to use a 20A stat to switch this?. Daughter's 2.5kw immersion still has the same 15A skol (or shol?) stat switching it for the last 16 years, so 15A switching 10.87A.
 
With reference to the 20A control stat I discovered this while searching for its technical specification:

Cotherm
TSD01106
Thermostat​

Cotherm TSD01106 20A Control Thermostat
A Cotherm brand adjustable control thermostat with a range of approximately 5°C - 85°C.
The TSD01106 is a rod thermostat with single pole break-on-rise action rated at 20A 240v. The stem (rod) is 265mm long and 7.5mm in diameter making suitable for use in all standard 280mm x 8mm (11" x 5/16") thermostat pockets. It is ideal for use in commercial products for direct control of single phase loads up to 3kW or to operate a contactor for higher loads or three phase applications.
Note: This device does not include a safety cut-out and is only designed to control the water temperature.
This thermostat is NOT SUITABLE for DOMESTIC without there bring an additional a safety cut-out as required by law.
Condition: New and unused in original manufacturer's packaging.

Delivery​

Orders received before 2pm Monday to Friday will be despatched the same day. Orders received after 2pm Friday, Saturday or Sunday will be dispatched the following Monday. Orders received after 2pm will be treated as having arrived the following day.

All goods are dispatched, professionally packed, on a signed for service. In most cases our carrier can leave the goods in a safe place, or with a neighbour for no extra charge. Should you require this service please detail it in the notes when placing your order together with a contact telephone number.

If you do not receive the goods within three working days (Monday to Friday) of placing your order we would ask that you contact us. We can then investigate the problem and authorise a replacement where necessary.

If you wish to purchase more than one listed item, we can usually ship these together for a reduced overall carriage charge. In this instance please contact us before paying so that we can advise you of the combined carriage charge.

Hours​

 
Last edited:
I have a 4kW immersion heater in a thermalstore - very recently replaced by a plumber as the previous one was leaking. Supplied with a cotherm thermostat and a second pocket for a safety cutout into which the safety cutout from the previous immersion was fitted and seems to be working fine.

I smelled burning and removed the cover to find that the insulation on the wire between the cutout and the stat was melting. The end closest to the stat was clearly more affected. The stat has deformed around the point the wire connects to it and the stat has ceased to work.

The wire between the safety and the stat is exactly the same as the wire from the spur to the immersion which has been in place since I can remember. The connection seemed sound but hard to tell now.

One thing I had noticed after it was installed is that it was cycling on and off quite rapidly.

Just a faulty stat?
One thing I had noticed after it was installed is that it was cycling on and off quite rapidly.

By the second it I reckon you mean the control stat. I think this control stat is acting akin to a thermal flasher device viz:

What is a Flasher Unit? | what is a Flasher Relay? - https://www.arc-components.com/blog/blinking-lights-what-is-a-flasher-unit.html

One might assume the control thermostat stat senses the temperature of only the water in the tank - but it does not. Alas the control stat will also be subjected to the Ohmic heating effect of all its electrical components through which the IH element current flows. This heating effect will increase if the IH element current is higher as is the case for a 4kW element vis a vis a 3kW one.
 
Last edited:

Reply to Immersion Thermostat wire burns out in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, I'm after some help please. I have a 21 panel 8.5kw system with 5kw export allowance and a Sunsynk 8kw inverter. The inverter has a smart...
Replies
0
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
we have a conventional heating system and underfloor heating recently installed by the builders plumber - it’s all wired up (pump, valve...
Replies
4
Views
2K
Hi, I bought a house that has a garage that was converted to an office by the previous homeowner, and it is separate from the main house. I...
Replies
3
Views
1K
Called to look at a job today for a previous client. Tumble Drier giving off 'funny smell' and tripped the RCD - Called out her appliance...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock