Cotherm TSD01106 Thermostat - 280mm Stem, 20AMP | eBay - https://www.ebay.co.uk/itm/183661179944

It was this company advertising on ebay to sell the control stat that included the advice I pointed out in red. Perhaps email or call them for further information. If you learn more from this company on why the advice was given would you mind sending another post so others can know too please?

Regards
Marconi

WH (Water Heating) Co Ltd
Trevor Guy
2 Horsecroft Place
Harlow
Essex
CM19 5BT

Phone: 01279641722
Email: [email protected]
 
Total resistance was measured at 14 ohms so 3 elements in parallel = approx 42 ohms/element but total current through stats is still the same, "4kw" immersion is 3.779kw @ 230V = 16.43A. or 4.114kw @ 240V = 17.14A so new stat is just doing what it's supposed to do and not burning out?. (single phase supply).
 
Last edited:
Wrote to supplier who replied:

The thermostats are designed for single phase elements, or three phase elements wired in single phase configuration up to 4kw.
To use with elements wired in three phase configuration, the thermostat needs to switch a contactor.
So, the thermostat you received with your 4kw element is suitable for single phase use.
The 4kw element is rated at 17.5a and the thermostat is rated at 20a.
We have never had a thermostat burn out. Please check your wiring as the problem is not with the thermostat.


However, it seems to contradict the instruction leaflet (not received with the immersion - emailed after) which seems to say that higher loadings than 3kW need a contactor?

1654707896882.png
 
I'm suspicious of the binary pricing of the Cotherm thermostat in the marketplace - around £12 general outlets, around £30 from reputable suppliers, one of whom publishes this footnote with the details of the stat:

SANTON S8203 THERMOSTAT TSD01106 11" 5-80'C COTHERM
This part is compatible for use with:

  • Santon DF range R25/R45/R70/R115
PLEASE BE AWARE: This a genuine Heatrae Sadia manufactured part, unlike many of our competitors.

The genuine part seems to have a 'properly approved' 20A resistive rating, so I would have thought capable of handling the 4kW load. Perhaps your leaflet covers the, dare I say, " Chinese Export" version 🤔
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

brixtonia

DIY
-
Joined
Location
England, UK.
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Immersion Thermostat wire burns out
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
brixtonia,
Last reply from
Avo Mk8,
Replies
34
Views
7,512

Advert

Back
Top