set up for immersion goes like this for me....

Option 1) 16amp breaker > 2.5mm t&e to 20amp DP isolator > flex from this to immersion.

But how is this set up.....

Option 2). 16amp breaker > 2.5mm t&e to 13amp fcu > flex from this to immersion

Are both fine?
 
If domestic no requirement for local isolation if on its own dedicated circuit.
 
Hi - Local 20A DP switch for immersion isolation is appropriate IMHO as work may be done in the vicinity by someone not familiar with boards etc. I use 2.5mm from the board as it has margin for installation Method 103 worst case.
 
Hi - Local 20A DP switch for immersion isolation is appropriate IMHO as work may be done in the vicinity by someone not familiar with boards etc. I use 2.5mm from the board as it has margin for installation Method 103 worst case.

So, good practice but not required.
 
What do the manufacturers instructions say? Or is this a theoretical question? Local DP switch for me also. If the voltage fluctuates that fcu will die. Seen it happen so many times. Also the local isolation helps Mr wet pants who’s either too stupid or too lazy to isolate elsewhere!
 
What do the manufacturers instructions say? Or is this a theoretical question? Local DP switch for me also. If the voltage fluctuates that fcu will die. Seen it happen so many times. Also the local isolation helps Mr wet pants who’s either too stupid or too lazy to isolate elsewhere!

Would you agree no actual requirement for local isolation
 
Local isolation is safer for anyone else working on the immersion heater in the future and also makes it easier for testing in the future.

A local isolator which is effectively under the constant supervision of the person doing the work is a safe isolation which doesn't rely on them having a lock off kit which many domestic workpeople don't. Also most circuits are rcd protected these days so the local dp isolation prevents tripping the rcd when N and 3 touch whilst working on the immersion.

And for testing the DP isolation allows you to test a suspect immersion heater without having to disconnect the neutral somewhere.
 

Reply to Immersion wiring and amp sizes in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock