Hi



I’ve just had a new kitchen and an induction hob installed which is on its own 32amp rcbo but my question is the total load rating is 7.35 for the induction hob which is just below 32amp if I’ve worked that out properly and it’s fitted to a cooker switch with a socket on which will have the microwave on as well so surely combined this would exceed 32amps, he used 6mm cable but should this be on a higher amp rcbo say a 40?



Also he’s put an outside socket in which is on a 16amp rcbo should this be a 32amp



I’ve not had any issues but I was reading the manual which got me thinking



Any advice appreciated
 
I'm guessing that is 7.35kW rating?

At 230V that would be 32A, however, it is rare for everything to be on maximum for any length of time in a domestic cooker, so the IET guidance for diversity (i.e. the reasonable-case use of several loads, in this case differing elements, etc) for a domestic cooker is:

10A + 30% of the remaining current + 5A if kettle outlet fitted

So in your case that would be 10 + 0.3*(32-10) + 5 = 21.6A and so a 32A breaker is OK.

Probably the same with the outside socket. Without knowing the cable choice, length, and if it is a single or double socket, it is not possible to see if larger breaker would be acceptable or useful, but it is very unlikely you would have 2 * 13A load there so having a 16A breaker would usually be reasonable for that. Most likely it will be used occasionally for a lawn mower at ~4A or whatever!
 
Many thanks for your prompt response

it is 7.35kw for the hob and to be honest I doubt it will ever have everything on

the outside socket is a double which is approximately 7 meters away from the consumer unit and is 2.5mm cable, it will be used 95% of the time for the lawnmower otherwise I might cut some wood with a mitre saw or similar

Thanks
 
The other factor that impacts a cable's current carrying capacity is if it runs through thermal insulation, a hot area, or if it is grouped with other cables. Best-case rating (single run of 2.5mm clipped to a wall) you could get away with a 25A breaker, more general case you would stick to 20A or less.

Realistically you are unlikely to ever go above even 13A on that outdoor socket.

Only typical domestic case where a double socket runs higher than 16A is a typical kitchen with two heavy loads on it (like a washing machine and a tumble dryer) that are often used simultaneously. I think most electricians would opt for two single sockets in that case though as you find doubles tend to show signs of thermal stress after a while.
 
Many thanks for your responses

this all makes more sense now

also the kitchen is on its own 32amp ring and he’s put singles on the washer, dryer and dishwasher like suggested so all seems well and it's reassuring that he’s done a good job
 

Reply to Induction Hob Query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
761
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
927
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
982
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...
Replies
10
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock