If the hob is on its own circuit and not incorporating a socket on the switch then surely the requirement for RCD can be omitted?


New circuit/chased in wall, so i cant omit the rcd unfortunately

it is a large hob, 800mm accross, 25a supply req. so required radial
 
It has solved the problem, but as i said to the customer, the hob must have an abnormally high earth leakage

i would not have though that by intentional design?

Certainly without some warning in the instructions
 
New circuit/chased in wall, so i cant omit the rcd unfortunately

it is a large hob, 800mm accross, 25a supply req. so required radial
Correct me if I'm wrong, and I'm often am, but cannot your apply diversity to this appliance when calculating the load.
I had a similar issue with an electric Aga range oven with an induction hob (15kw total load). It was being reinstated into a kitchen refurbishment. The original connection (old kitchen) had been done by Aga engineers, and had been happily running on a 32amp supply. Checking with Aga about the total load for their appliance, they recommended 45amp supply. I mentioned diversity, which was met with silence. So hedging my bets, I installed 10mm cable (only 3m from CU) with 32amp breaker, and have had no probs with it (touch wood).
 
Having just researched this subject on the net, loads of hits on induction hobs/earth leakage & RCD's tripping. Seems a lot of manufactures recommend putting induction hobs on their own circuit/RCBO for that reason.

What do you guys do (apologies OP for hijacking your thread, but may also answer your question)? I ask because I have an install forthcoming for separate oven & induction hob, and I was going to use one radial for both?
 