I've got to earth a new 50mm steel gas pipe.
The pipe fitter didn't fit an earth stud to it and now he's gone.

Am I just looking at a large earth strap or something else?

Any ideas are welcome?
 

Attachments

DPG

-
Arms
Esteemed
That copper pipe looks like it goes a fair distance without any support.
 
  • Thread Starter Thread Starter
  • #11
Due to a supplier delay, the gas pipe is now bonded via welded studs.

16mm earth via a stud on the pipe within 600mm of the consumer side.

Also cross bonded over joints too.
 