Well took a little longer to get here but seems we’re running a 35mm earth cable through the wall and expanding an earth block that was hidden away in the distribution room, seems weird even back in the 80s that they just put a 6mm earth cable from the consumer unit to the isolator but guess it must have been ok back in the day!
I haven’t, the man in the know has, I thought he said 25mm before but he’s told me to get enough 35mm in to go through the wall into the meter cupboard where he’s connecting it in somewhere