Among other things,the new boards breakers,layout,rcd's,tails and bonding will all have changed since you did the EICR so even for those reasons then you'll need a EIC. As well as notify 'Part P' farce.
I understand that but by adding what u have listed would improve the safety of the installation. Having done the eicr , you would know that the final circuit are ok and by adding rcd protection your maximum zs would be higher.
Charging for 2 certs to change a board wont get many jobs
Yes but time is money , to carry out an eicr thoroughly , type it up then change a board takes time. Never mind going through the same test again and typing them up
If you are changing consumer units you should understand the requirements for certification for the job. This seems to be a problem of your own making trying to do a full EICR and a CU change in the same day.
You can ascertain the information required for swapping a CU without doing an EICR.
What regulation says you must do an installation cert after changing a board?
Good practice guide says you should do it but im only asking why i should Have to do an installation cert after i have done an eicr which is more thorough and i havent installed any circuits.