Discuss Installing earth rods should be totally buried in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
55
I read a couple of references to ground rods and both stated that they must be buried in the ground but one said 3 inches visible and the other said less than 12 inches visible.
I thought they had to be fully buried and even covered .

Please confirm I’m correct z(for once!)
 
The end of the rod needs to be above ground for connection to be inspected and serviced.

buried in the ground is a poor choice of phrase, it suggests that you can lay them in a shallow trench and back fill.

they should be driven to a depth with some exposed rod to connect to.
 
Thanks for replies. I thought that if the rod is at ground level then the voltage could be as high as 25 volts 2.5-3 metres from the rod ( a danger to animals ) etc. I thought that it needed to be in a pit with inspection cover.

And I agree that buried was not a good choice of wording. ( driven into the ground is better)
 
I read a couple of references to ground rods and both stated that they must be buried in the ground but one said 3 inches visible and the other said less than 12 inches visible.
I thought they had to be fully buried and even covered .

Please confirm I’m correct z(for once!)
Had these rods been installed, inspected tested in the correct manner using the correct testing equipment??
 
If driving a 1000mm rod in 300mm gives a reliable Ze then nothing wrong with leaving 700mm sticking out (not that anyone would leave it like that ....... would they?) ...... certainly seen some 200-300mm above ground though!
As post #2 though the end termination must be accessible for inspection/testing, in a readily available box.
 

Reply to Installing earth rods should be totally buried in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
953
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi everyone, I've been asked to install a consumer unit in a summer house with circuits for light and power. The owner has already laid SWA...
Replies
4
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock