If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Spouse of an advanced city and guilds electronics Lab technician (retired) and DIYer
I read a couple of references to ground rods and both stated that they must be buried in the ground but one said 3 inches visible and the other said less than 12 inches visible.
I thought they had to be fully buried and even covered .

Please confirm I’m correct z(for once!)
 
The end of the rod needs to be above ground for connection to be inspected and serviced.

buried in the ground is a poor choice of phrase, it suggests that you can lay them in a shallow trench and back fill.

they should be driven to a depth with some exposed rod to connect to.
 
Thanks for replies. I thought that if the rod is at ground level then the voltage could be as high as 25 volts 2.5-3 metres from the rod ( a danger to animals ) etc. I thought that it needed to be in a pit with inspection cover.

And I agree that buried was not a good choice of wording. ( driven into the ground is better)
 
I read a couple of references to ground rods and both stated that they must be buried in the ground but one said 3 inches visible and the other said less than 12 inches visible.
I thought they had to be fully buried and even covered .

Please confirm I’m correct z(for once!)
Had these rods been installed, inspected tested in the correct manner using the correct testing equipment??
 
  • Like
Reactions: James
Had these rods been installed, inspected tested in the correct manner using the correct testing equipment??
These cases were documented but they didn’t say whether they were inspected.
I realise that this would be done though one of the cases was not in the u.k.
 
If driving a 1000mm rod in 300mm gives a reliable Ze then nothing wrong with leaving 700mm sticking out (not that anyone would leave it like that ....... would they?) ...... certainly seen some 200-300mm above ground though!
As post #2 though the end termination must be accessible for inspection/testing, in a readily available box.
 
  • Like
Reactions: James

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Stevenage
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Spouse of an advanced city and guilds electronics Lab technician (retired) and DIYer

Thread Information

Title
Installing earth rods should be totally buried
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Ziggie,
Last reply from
Macsamillion,
Replies
6
Views
6,837

Advert