Discuss installing temporary 110v supply for a transformer in the Australia area at ElectriciansForums.net
K
kyranocat
hi guys could really use some help have been given task on my practical course of installing a temporary supply for a 110 tranny, i am either thinking too much or really thick at getting my head around it, i thought seeing as there is a spare consumer unit in the test rig i would install a 32amp mcb with rcd protection and one socket in 2.5mm2 radial. does this sound like its protected enough i mean with a 110v tranny the current carrying capacity should be enough? or am i stupid?
any help would be appreciated.
What is the KVA rating of the transformer and does it have a fuses on primary or secondary winding?
What will be the expected demand from the supply?
Start with the load which is the transformer and work backwards to the CU. The transformer size will determine the cable size and the cable size will determine the MCB size in the CU.
3.3KVA is fine on a 2.5mm cable between the Tx and the CU. A 20A MCB would be appropriate.
If the socket is 13Amp rated it's a bit shy, you could install a 16Amp Euro type socket or it might be better to connect the Tx via a fused DP switch unit or DP isolator. I'm sure one of the UK guys will give you the best option.
Unless its loaded right up to its maximum the OP may just get away with an extension cable from a standard RCD protected socket. Always allowing for coiled cables etc.
Come to think of it thats what I use on site most of the time....:smilewinkgrin:
my 3.3kVA site tranny almost invariably trips a 16A type B on switch on surge. a16A or 20A type C is what i recommend, on a 2.5mm radial.
thanks guys i appreciate the help its already mentioned at the back of the wiring regs for a 20amp breaker on 2.5 mill cable for radial but i just wanted to make sure , i was going to start with design current etc and work it out to be sure but no idea what the wattage etc is gonna work out to unless i assume an approx amount then again its hand tools that need powering unless the cheeky ******* plans on powering a factory with it in which case it seems fine.
Reply to installing temporary 110v supply for a transformer in the Australia area at ElectriciansForums.net
Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...