Was wondering if you could clear up a few things I on't quite understand, I've been told it is possible to do an insulation resistance test on a live DC cable (Solar pv) by testing to ground. Is this right, and what voltage rating should I set the megger to?

Also on a domestic solar pv installation would you test to earth on the consumer unit?

Also how is the voltage given out by the megger affected by the voltage in the circuit? and vice versa.

Confusion reigns:mad2:
 
Hi

Was wondering if you could clear up a few things I on't quite understand, I've been told it is possible to do an insulation resistance test on a live DC cable (Solar pv) by testing to ground. Is this right, and what voltage rating should I set the megger to?

Yes, and voltage set should be in line with Table 61 of BGB

Also on a domestic solar pv installation would you test to earth on the consumer unit?

Yes, that could be the same as the 'ground' mentioned above, you should also test to the array metalwork.

Also how is the voltage given out by the megger affected by the voltage in the circuit? and vice versa.
If you connect the megger to one side (+ or -) only and to earth it doesn't see the PV voltage (or shouldn't) as you are not completing the circuit!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Insulation resistance on a live DC cable?
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
mikemack00,
Last reply from
yellowvanman,
Replies
1
Views
4,194

Advert

Back
Top