Doing an insulation resistance test on a shower, can someone explain how to bypass the neon in the isolator? Do most people chock block bypassing neon or another way?
Also for a lighting circuit with flurocents?
Thanks
 
When doing an insulation resistance test on most circuits with a load across live and neutral, you need to put one probe of your tester to live and neutral at the same time and the other probe to earth. No chock blocks needed at switches or isolators. :) I just remembered, in a lighting circuit with a dimmer switch you need to bypass the dimmer switch.
 
Last edited:
Shouldn't need to, are you doing an EICR. Just carry out the test to earth only omitting the line/neutral test.
 
Doing an insulation resistance test on a shower, can someone explain how to bypass the neon in the isolator? Do most people chock block bypassing neon or another way?
Also for a lighting circuit with flurocents?
Thanks
L and N linked test to earth
 
When doing an insulation resistance test on most circuits with a load across live and neutral, you need to put one probe of your tester to live and neutral at the same time and the other probe to earth. No chock blocks needed at switches or isolators. :) I just remembered, in a lighting circuit with a dimmer switch you need to bypass the dimmer switch.
OT big time I'm afraid so apologies. Had8Lives - is your pic a silver studded blue?

View attachment 35544
 
That's why the Crabtree pull switches are so good, drop the cover down and the neon is disconnected. Pointless though if the shower has always on neons etc.
 