HappyHippyDad

~
Arms
Supporter
Good morning all..

My customer has has a Masterchef Deluxe 110 Dual Fuel cooker.

The ovens, grills and warming draw are all electric. The hob is gas, the cooker itself supplies the electrics for the ignition for the gas (i.e it is not plugged in separately.

I changed the consumer unit for an RCBO board. Since then the cooker has started tripping. It did not have RCD protection before.

It is on a 32A RCBO.

It doesn't trip when switched on.
The last time it tripped they were just using the gas burners and the warming draw, however it seems as though it tripped after they had finished using these and they were switched off
Another time it tripped neither of these were being used, and it was just the left hand oven. Again, it tripped when she physically switched the oven off (using the dial, not the main switch)

So it seems to trip with various parts being used.

This tripping cannot be re-enacted. She has tried using the left hand oven, and switching it off does not make it trip again. It seems it only did this once.

IR results for the cable, all the way to the cooker is >999Mohms, L-E, N-E and L-N
IR results on the cooker itself were also high (cant remember what, but many millions of ohms)

They have had 2 cooker engineers out who could find no problems with the cooker. It even tripped in front of one of them.

I have just had a thought. I'm so preoccupied with the cooker, because RCBO's are hardly ever faulty. Maybe just try changing the RCBO? I realise it's not going to be that, but it's worth ruling it out.

Opinions please?
 
Last edited by a moderator:
Domestic appliances often switch their component parts in the neutral for reasons better known to themselves, so a faulty component is still connected, even when 'off' on its control. If IR testing doesn't show anything (it often doesn't with an element), then you'll have to resort to taking the back panels off and disconnecting a single element completely until you can be reasonably sure that the tripping has stopped.
The most obscure range cooker fault I've had was where one of the oven elements had been changed for a pattern one some time previously, but this had placed the element terminals closer to the inside of the back panel when it was refitted. The back panel would 'move' a little in response to heat from the oven, and very occasionally, touch the panel.
Close examination revealed a tiny black burn mark on the inside of the panel.
Cure was to place the panel against the end of a bit of 3" steel tube, with the burn mark centred, then knock seven bells out of the steel with a ballpein hammer. Back panel now has a convex dome on the back of it in the appropriate place.
 
When the RCBO trips, can it immediately be reset?

A slight downside to RCBOs is you can't tell if it's an earth fault, or overcurrent. Temporarily changing the RCBO for an MCB, with a separate RCD just downstream, can help you identify which it is.
 
Domestic appliances often switch their component parts in the neutral for reasons better known to themselves, so a faulty component is still connected, even when 'off' on its control. If IR testing doesn't show anything (it often doesn't with an element), then you'll have to resort to taking the back panels off and disconnecting a single element completely until you can be reasonably sure that the tripping has stopped.
The most obscure range cooker fault I've had was where one of the oven elements had been changed for a pattern one some time previously, but this had placed the element terminals closer to the inside of the back panel when it was refitted. The back panel would 'move' a little in response to heat from the oven, and very occasionally, touch the panel.
Close examination revealed a tiny black burn mark on the inside of the panel.
Cure was to place the panel against the end of a bit of 3" steel tube, with the burn mark centred, then knock seven bells out of the steel with a ballpein hammer. Back panel now has a convex dome on the back of it in the appropriate place.
Wow, that was a good bit of fault finding.
 
When the RCBO trips, can it immediately be reset?

A slight downside to RCBOs is you can't tell if it's an earth fault, or overcurrent. Temporarily changing the RCBO for an MCB, with a separate RCD just downstream, can help you identify which it is.
It previously was on an MCB, with no RCD protection. It was absolutely fine.
In addition, it tripped at one point with just the 1kw warming draw on, so it's not an overcurrent problem.
 
MCB tripping only faults are usually easier to find than anything that's RCD protected, due to the 'let through energy' dissipated at the site of the fault. If there wasn't a RCD to trip, my cooker back panel would probably have had a hole blown in it.
 
MCB tripping only faults are usually easier to find than anything that's RCD protected, due to the 'let through energy' dissipated at the site of the fault. If there wasn't a RCD to trip, my cooker back panel would probably have had a hole blown in it.
I'm not sure if I explained it well.
It was previously on an MCB, with no RCD protection and there was no tripping problem.
Since then, i have changed the consumer unit for an all RCBO unit. It has now started tripping.
 
Low reading clamp meter round line and neutral only and get someone to operate controls while noting readings for leakage, ramp and time test the rcbo.
Or more risky temporary disconnect cpc and measure voltage from met and the cpc
 