markadams

Hi,

I have recently replaced (like for like) three outside lamp post type lights, when I came to do the testing I couldn't remove the bulb from one of the old lights so decided to do an IR test between Line-CPC and Neutral-CPC. I was surprised to get 0.18 on both tests. The circuit was disconnected from the supply so that was not giving a false reading, its the result I would have expected from the Line-Neutral test with the bulbs in.

Due to this I struggled and managed to remove the bulb and it retested fine >200 on 250v and >500 on 500v

I have done this test before with no problems, anyone know why this didn't work?

Mark.
 
did youplant the bulbs after you took them out? :lipsrsealed2:
 
Hi,

I have recently replaced (like for like) three outside lamp post type lights, when I came to do the testing I couldn't remove the bulb from one of the old lights so decided to do an IR test between Line-CPC and Neutral-CPC. I was surprised to get 0.18 on both tests. The circuit was disconnected from the supply so that was not giving a false reading, its the result I would have expected from the Line-Neutral test with the bulbs in.

Due to this I struggled and managed to remove the bulb and it retested fine >200 on 250v and >500 on 500v

I have done this test before with no problems, anyone know why this didn't work?

Mark.


Any control gear in these fittings, could be when you took the bulbs (sorry lamps) out you dissed some of the control gear out of circuit. just a thought.
 
Any control gear in these fittings, could be when you took the bulbs (sorry lamps) out you dissed some of the control gear out of circuit. just a thought.

No control gear at all, just SWA to a connector block then flex straight to the Lamp holders (I have woken up now).
 
No control gear at all, just SWA to a connector block then flex straight to the Lamp holders (I have woken up now).

In your post you said you had 2 > than readings when you did the IR test 200 and 500 I think, can't understand how you managed to get those 2 readings.
 
Tested at 250v with lamps out I got >200Mohms, then did the test again at 500v and got >500Mohms. tested at the disconnected start of the SWA cable.
 
Tested at 250v with lamps out I got >200Mohms, then did the test again at 500v and got >500Mohms. tested at the disconnected start of the SWA cable.

How much of a problem would it be to disconnect the SWAs at each of the fittings and test the cable, then if all is well test the flexes with the lamps out up to the lampholders.
 
No problem for the first three as they are new, but the last two are old and corroded. The SWA must be OK as it tests fine with the lamps removed. It looks like the customer is going to have the other two replaced so I will investigate more as I am curious what is happening.
 