There's a duplicate thread in DIY with the same subject, but neither has the full information.
 
  • Like
Reactions: benhurr and DPG
Interesting. The way I read table 52.3, from left to right, 0.75mm2 flex is permitted.

Do you mean the bottom section for single appliances and other applications?

It is my understanding that this really relates to the final aspects, such as pendant drops etc rather than fixed wiring
 
Do you mean the bottom section for single appliances and other applications?

It is my understanding that this really relates to the final aspects, such as pendant drops etc rather than fixed wiring
I do indeed mean the bottom section, but I have selected 'flex' from column 1 first, then 'any other application' from col 2 (I assume this means 'any application other than those others listed for flex'), which gives me 0.75mm2 from col 3.

It seems logical to me to work from the table in this order, rather than working from the middle outward (though the table really could be clearer on this).

I had also assumed that the minimum 1mm2 was for non-flexible cables due to smaller conductors being prone to damage, either during installation or in use, whereas this wouldn't be a problem for flexible cables.
 
  • Like
Reactions: benhurr

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
harrow
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Fan (4w)?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
benhurr,
Last reply from
Pretty Mouth,
Replies
22
Views
3,604

Advert